Hi all just wondering if I could pick you brains, I was doing a ze today on a consumer unit, 80amp rcd main switch, (the test button wasnt functioning so I was already thinking as to what caused this to blow) I disconnected the main earth, turned the main switch into the off position, I then went to test between line and earth & as soon as I put the probe in the live terminal its blew the main switch & my probe completely, any idea as to why this happened? Im yet to come across an issue when carrying out a ze test, cheers.
 
From the little info given, the pertinent questions (already asked) seem to be what tester do you have and are you sure it was not in continuity or IR modes when you put the probes on?
 
From the little info given, the pertinent questions (already asked) seem to be what tester do you have and are you sure it was not in continuity or IR modes when you put the probes on?
Hi I have a dilog multi meter, it was in ze mode, ive tested other properties all is fine, I switched off the main switch, disconnected the pain earth, as soon as I put a probe in the incoming live terminal the switch sparks and blows, it also took the end off my probe
 
Your post is a little sketchy as to what you have done
What exactly do you mean by blew the main switch and my probe, I'm assuming you were testing on the incoming side of the main switch when this happened
Does your meter still function and what model is it
Meter still in working order, I was testing on the incoming line amd main earth, it sparked, bamged and blew the end off the probe as soom as I inserted the probe into the line terminal, the main switch was off, could this be a dodgy main switch rcd as the test function was not initially working
 
Hi I have a dilog multi meter, it was in ze mode, ive tested other properties all is fine, I switched off the main switch, disconnected the pain earth, as soon as I put a probe in the incoming live terminal the switch sparks and blows, it also took the end off my probe
Can you do a PSSC on incoming live and neutral to prove the meter (and leads and probes) still function? Are they fused leads or just a fused MFT [I'm assuming here]?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South wales

Thread Information

Title
Rcd Main switch blown by Ze test
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
Mikey10695,
Last reply from
plugsandsparks,
Replies
14
Views
2,674

Advert

Back
Top