Hi All, update on the assessment I had today.
I explained to the assessor that the lighting circuit had no cpc and that I had advised client and replaced metal fittings with plastic pendants. He was fine with that and said he’d done the same in the past when he was on the tools. He said if the...
Thank You. I just put both ends in wagos and flagged cable ‘do not terminate ‘at CCU.
Murdoch I didn’t ask for a discount as didn’t want to irritate them before the assessment but I will ask for one after,as if I had of cancelled it would have cost me money. I think Saturday assessments is...
I’ve sorted the neutral fault. Was one of the legs back to the board strangely. I’ve disconnected both ends made safe and reduced to a 20 amp breaker. I’ve also swapped the metal fittings for pendants. The assessor had to cancel the visit and rescheduled for next Saturday. So gave me time to...
The kitchen actually has two rings to it. As is an old extension and assuming from when this was done. I haven’t established which outlets the break is between yet.
Cheers Gavin. I don’t get precious about constructive criticism. I kind of expected what the response to the post would be.
Hi Murdoch 100Amp BS7671. Was 25mm already to meter from fuse. I upgraded to 25mm from 16mm load side of meter. Main Earth already 16mm, bonding to gas and water already...
The job is neat and tidy and meets all other criteri apart from the issues. I’ve actually since spoken to the client and they’re happy for me to sort out Thursday. I’ll keep you posted on how I get on with assessment. Cheers all.