can anyone tell me if this is a correct way of thinking
i have 6 Cleaners outlets off a !6a rcd, total run length is 55m
6mm feed to first point is 30m would give me voltage drop of .78% (using half the breaker load according to exception 1 on page 163 of as 3000:2018)
then run a 2.5mm for...