My house is off-grid and supplied from an inverter. Max power output of the inverter is about 6kW (25A). Max fault current is 100A. The highest rated Type B MCB that can be tripped by this max fault current is 16A, so I cannot use MCBs with higher ratings than that. I cannot have a circuit with...