Recent content by Phil1234

  1. P

    UK MCBs for Inverter-Supplied System

    It's a TN system. Neutral and Earth are connected at the inverter output and are also connected to an earthing rod.
  2. P

    UK MCBs for Inverter-Supplied System

    Thanks for the advice Julie, I'll look into the manufacturer's data for MCBs.
  3. P

    UK MCBs for Inverter-Supplied System

    My house is off-grid and supplied from an inverter. Max power output of the inverter is about 6kW (25A). Max fault current is 100A. The highest rated Type B MCB that can be tripped by this max fault current is 16A, so I cannot use MCBs with higher ratings than that. I cannot have a circuit with...