Hi all,

I’m looking for some clarification on RCD requirements regarding EICR reports in the UK.
This is for a standard office that was built in 2007 and is used by IT workers.

We've had an EICR review and been told that we need RCDs for all circuits apart from those locked in the server room.

My questions are:

1. Can we just complete a risk assessment, without installing RCDs, and still pass the EICR?
2. If we need to install RCDs, do we need to install them on all circuits?
3. Are there any scenarios where we don't need RCDs to pass the EICR?

I’d really appreciate the views of electricians who carry out EICRs regularly.

Thanks in advance!
 
It would depend on who does the EICR and their opinion of RCDs for general socket outlets. Assuming fault protection is maintained without them and the socket outlets are not likely to supply equipment for use outside it is generally considered a Code 3 for 30ma (additional) RCD protection.
 
  • Like
Reactions: sparksfly
It would depend on who does the EICR and their opinion of RCDs for general socket outlets. Assuming fault protection is maintained without them and the socket outlets are not likely to supply equipment for use outside it is generally considered a Code 3 for 30ma (additional) RCD protection.
Thank you for your advice and for confirming what I thought.
I have been reading the Electrical Safety First best practice guide 4 and this suggests it is a C3 for our scenario as well.
I will discuss it further with the electrician.
 
  • Like
Reactions: DPG and westward10
It would be well worth discussing as electricians often put a Code 2 against this then you are stuck with it.
 
I personally err towards C2 when dealing with lack of 30ma RCD protection. Not in every case, but more often than not.

Also, if you are registered with Napit, they have clear expectations of what codes should be given. I realise we don't have to agree with them, or even adhere to them, but if you are registered with Napit you do find yourself moving towards the 'codebreaker' suggestions. C2 for cables in zones, in a wall <50mm, no 30mA RCD protection.
I do actually agree with this one.
DIY'ers are always drilling through cables directly above or below sockets, to hang their new shelves.
 
  • Like
Reactions: DPG and 7029 dave
I thought if IT equipment was the primary user of sockets in an office and if unwanted tripping could cause damage and or loss of data and are labeled and risk assessed as use for the use of that particular equipment only then RCD coverage can be omitted?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Office Manager responsible for building maintenance

Thread Information

Title
EICR – Are RCDs always required for a satisfactory report?
Prefix
UK 
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
eicr

Advert

Thread statistics

Created
OfficeManager,
Last reply from
EddieB,
Replies
5
Views
292

Advert