been asked to price up and install some cable for a farm...etc..
my 3 phase calculations are a bit rusty so trying to brush up....
NEDL Have dropped a 50kva supply in on 3x35mm incomers..!
first part of job is to wire a TP&N Isolator to there meter tails so they can sign job off and allow me and the farmer to then proceed with deciding what he wants..!
just checking im right here... Kw = KVA / PF ..... im led to believe that NEDL told the farmer PF is 0.98 so quite negligible in this scenario...
so deciding on what size Isolator to install i would assume that
50000/230 = 217A
217/3 = 72A per phase
which ties in nicely with NEDL paaper work of 70 Amps per phase (correct me if im going wrong.. please)
as for the isolator i will be fitting a 100A TP&N (any body got preference on brand???)
never been asker to work out the design of 3 phase circuits so its all new and i dont want to screw it up hence getting head back in books again to read up on stuff that you brain forgets!
seems pretty easy and self explanatory but just rusty!!
my 3 phase calculations are a bit rusty so trying to brush up....
NEDL Have dropped a 50kva supply in on 3x35mm incomers..!
first part of job is to wire a TP&N Isolator to there meter tails so they can sign job off and allow me and the farmer to then proceed with deciding what he wants..!
just checking im right here... Kw = KVA / PF ..... im led to believe that NEDL told the farmer PF is 0.98 so quite negligible in this scenario...
so deciding on what size Isolator to install i would assume that
50000/230 = 217A
217/3 = 72A per phase
which ties in nicely with NEDL paaper work of 70 Amps per phase (correct me if im going wrong.. please)
as for the isolator i will be fitting a 100A TP&N (any body got preference on brand???)
never been asker to work out the design of 3 phase circuits so its all new and i dont want to screw it up hence getting head back in books again to read up on stuff that you brain forgets!
seems pretty easy and self explanatory but just rusty!!