Discuss 3 Phase.. calcs and bit rusty!! in the Australia area at ElectriciansForums.net
DurhamSparky
been asked to price up and install some cable for a farm...etc..
my 3 phase calculations are a bit rusty so trying to brush up....
NEDL Have dropped a 50kva supply in on 3x35mm incomers..!
first part of job is to wire a TP&N Isolator to there meter tails so they can sign job off and allow me and the farmer to then proceed with deciding what he wants..!
just checking im right here... Kw = KVA / PF ..... im led to believe that NEDL told the farmer PF is 0.98 so quite negligible in this scenario...
so deciding on what size Isolator to install i would assume that
50000/230 = 217A
217/3 = 72A per phase
which ties in nicely with NEDL paaper work of 70 Amps per phase (correct me if im going wrong.. please)
as for the isolator i will be fitting a 100A TP&N (any body got preference on brand???)
never been asker to work out the design of 3 phase circuits so its all new and i dont want to screw it up hence getting head back in books again to read up on stuff that you brain forgets! :)
seems pretty easy and self explanatory but just rusty!!
Just don’t do my mates trick. He found great place to kip, on the cable trays in the loft of a switch room, nice and warm. He rolled over, fell of the tray, through the ceiling, landed on the switchgear, fell off that and landed on the floor in a heap. Off work for a month with a bad back! I’m just glad I wasn’t the shop steward at that time.
i worked it out slightly differently steve, but got pretty much the same answer. im gona write it down here, as it may help others, if im right.
if im wrong, then others will realise im an idiot.
kva= kw x power factor, so this means alos that kw= kva/power factor
kw= 50,000/ .98 = 51020 = 51.02kw.
I= P/V = 51020/400= 127.55A
127.55/1.732= 73.6 A per phase.
Reply to 3 Phase.. calcs and bit rusty!! in the Australia area at ElectriciansForums.net
H
Morning all, Been asked by a mate to drop a cooker circuit in to a commercial unit. Not having dealt with 3-phase cookers before, thought it best...
14K
hightower
H
Hi guys, not longed joined and kind of glad I found this forum as its got so much info and help its awesome. Im about to do my practical for...
spartan_spark
Hello Im confused, thats not hard though. Working in France(dont read too much into that), they give specific guidelines to follow so you dont...
J
A customer of mine has booked a meter upgrade from 100a single phase to a 100a 3 phase meter so we can add an industrial oven to the system. the...
Knobhead
K
N
Hi all. Prospective Short Circut Curret. Now , if you measure the impedance on a installation P to N , and get a reading of 0.21 OHMS , the max...
Knobhead
K