I want to add a little builders consumer unit next to the main board, an RCD main switch and 2 x 32a CB's what size tails will I get away with? 25mm is not practicle given the size of the unit. I was thinking on the lines of 16mm. Is there a reg that governs this scenario
 
I'd agree with Mark. And to be honest, I wouldn't even consider anything else.
If it's not possible with the current consumer unit. I'd fit a slightly larger sub board and move one of the other circuits over. Something low draw like a lighting circuit.
 
The possible loading on the tails is limited to the combined size of the mcbs hence 64amps so 16mm tails is fine and we all know the circuits are not going to be loaded to the top anyway.
Its the same as a seperate shower board where you can feed it in 10mm tails because the 40/45a mcb limits the load that can be pulled through the tails.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

EddieB

Arms
~
Joined

Thread Information

Title
Additional consumer Unit
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
EddieB,
Last reply from
bugsy,
Replies
7
Views
1,983

Advert