@danielz000 if marconi is offering to come and help, I would jump at the chance. His Knowledge is vast. You may not understand a 100% of what he is explaining to you though ?.

Ps.. I love @Lucien Nunes explanation of why a standard resistance test from each end may well not work! (i.e pin hole and filling channel tunnel). Really helps you see the problem, especially when you cannot understand all of the physics involved.

I might understand somewhere in the region of 5% on a good day (plenty of sleep and a decent meal the night before).

Hopefully the OP jumps at this chance and then reports back here on the experience.
 
I might understand somewhere in the region of 5% on a good day (plenty of sleep and a decent meal the night before).

Hopefully the OP jumps at this chance and then reports back here on the experience.
If I'm interpreting it correctly the voltage drop (across R1+R2) is measured between the two ends of the faulty cable and then between one end of the faulty cable and the armour (just R1), one of the healthy cables is just being utilized as a 25 meter M.meter lead for the first reading. Not quite sure about the right calcs but assuming that the fault is say only 5 meters from the joined ends then the volt drop across RI might be V1x20/25. Would love to see actual test readings from this method.
 
If I'm interpreting it correctly the voltage drop (across R1+R2) is measured between the two ends of the faulty cable and then between one end of the faulty cable and the armour (just R1), one of the healthy cables is just being utilized as a 25 meter M.meter lead for the first reading. Not quite sure about the right calcs but assuming that the fault is say only 5 meters from the joined ends then the volt drop across RI might be V1x20/25. Would love to see actual test readings from this method.
I will do you a demo. All a bit academic now cos two joins underground not great future for this run of swa cable- one maybe tolerable but two …,…
 
I must have a go at that Varley test. I have a fault on a 4 core swa , 2 cores low resistance to each other and to earth. Would be cool to find the location of the fault, though most of the cable is now under a building extension. I do have a 20A variable PSU and some big resistors and power variable resistors
 
If I'm interpreting it correctly the voltage drop (across R1+R2) is measured between the two ends of the faulty cable and then between one end of the faulty cable and the armour (just R1), one of the healthy cables is just being utilized as a 25 meter M.meter lead for the first reading. Not quite sure about the right calcs but assuming that the fault is say only 5 meters from the joined ends then the volt drop across RI might be V1x20/25. Would love to see actual test readings from this method.
Most of the methods are doing this - establishing the resistance either side of the fault to armour. The different methods really come down to available test equipment, etc, and some minor variations in accuracy for a given assumption of test equipment, simil;arity of available 2nd conductors, etc.

One method mentioned that is not doing that is time-domain reflectometry (TDR) where a pulse is sent down the cable and where it encounters a change of characteristic some of it is reflected back. By measuring the time taken for this first reflection (you get another large one when the pulse reaches the far end) you can estimate the distance to the fault either directly (using the known velocity factor for the insulation) or by ration (from known length and far-end delay).

This is commonly used in RF systems but often indirectly (not a pulse, but maths performed on a swept-frequency reflection measurement), and in fibre optics using a laser pulse. Whereas in power systems they originally used the closing and then fault-triggered reopening of the supply breaker to generate the surge, though probably these days it is a safer low energy plust that is used!
 
I must have a go at that Varley test. I have a fault on a 4 core swa , 2 cores low resistance to each other and to earth. Would be cool to find the location of the fault, though most of the cable is now under a building extension. I do have a 20A variable PSU and some big resistors and power variable resistors
Let us know how you get on with the different methods, would be good to have some hands-on experience of how easy each/any of them were.
 
Overall though the underlying problem was most likely poor workmanship.

While you can bury SWA directly in the ground it should have sand or similar around it for several cm to make sure that sharp stones are not crushing the armour - there is always a limit to what it can take! Though it is just possible that very bad handling of the cable might have caused internal damage.

As others have also said, putting in duct is better for many reasons, though it also should have sand or very fine gravel surrounding it for the same physical protection reasons. The big advantages are: less likely cable damage, the ability (if sane length and route) to pull through a fault cable and bring its replacement in, and also to allow other cables if needed (say network for internet, etc).

Finally it should have been properly tested after initial burial and before final work over that area. And that means a proper high-voltage insulation check as well as the typical conductor / armour resistance chances you would do to verify any new circuit.
 
I must have a go at that Varley test. I have a fault on a 4 core swa , 2 cores low resistance to each other and to earth. Would be cool to find the location of the fault, though most of the cable is now under a building extension. I do have a 20A variable PSU and some big resistors and power variable resistors
I do not have a long length of swa with which to do a realistic demo using a high current. How about me sending you my test rig - the parts for which are on order and due today - and then you use it on your defective length of swa cable and see how it performs in practice? You can keep it afterwards.

What is the csa and length of your cable?
 
Yes I would be interested in playing with your bits! The CSA is 25mm2 length ~40M. Someone with some modern test gear was going to take a look last week but couldnt make it. I ended up retesting the 2 undamaged cores at 2500V today to prove they were still ok, got greater than 2500Mohm in all directions once I had cleaned the exposed insulation in the cabinet outside, as needed to get a reduced supply back on feeding half of the lighting. The fault is between yellow and red phases and armour today it measures around 100ohms on a continuity test. The 2 damaged cores are now extra cpcs. As most of the cable route is now built on it is likely a new route will have to be dug soon. A ground working company are looking in next week.
 
I will start to assemble the test rig tomorrow afternoon. I assume you have some jump leads to connect a 12 V battery to my board and a digital voltmeter able to read 12V dc. As the cable is 25mm2 I will arrange to produce some pulses of current of the order 70 to 80 Amps so that a volt drop of a few volts is produced along the red or yellow conductor. I am using twenty or so 12V 50W halogen lamps as my power resistors so you will need to wear some sunglasses when it pulses the current!
 
Good. One last question - what is the settling time of your dvm? Ie, if you measure the terminal voltage of one of the 12V batteries how many seconds from making contact before the digital readout remains constant?
 
Can you video this testing out of interest?

Also it would be interesting to compare the measurement results of a couple of methods to see how closely they agree, and potentially to compare that to where the fault is finally located if the cable is dug up at some point.
 
Semi-related interesting video.... I'm not suggesting this is the way forwards but it's VERY cool....
With external power source (up to 40v before resistors needed) this would actually do the Varley test as far as I can see.
 
Prototype 12V 25A load.
 

Attachments

  • 56081CC8-25D8-47A9-B44C-47B8718C60E7.jpeg
    340.7 KB · Views: 19
This test rig is a demonstrator not some finished item of test equipment so its construction is economic using many items just gathering dust in my man shed.

The interesting aspect of this project for me is not so much the method which is long established it is actually doing it practically. The hardest part of it is finding a cheap way to load up a 12V battery to cause a current of the order of 75 Amps to flow without everything bursting into flames or becoming a molten mess. In other words the power resistors. Hence my use of 12V 50W g6 halogens. The nice thing about these is that once lit their current is quickly constant during the test unlike using other resistors - and cheap.

Nevertheless, there will be 18 x 50W halogens lit producing mostly heat and some light - nearly a kW. You can see from the image I posted that I used cheap connector blocks - I could not find online a way of buying a score of g6 lampholder with leads without spending a small fortune. So I improvised. But by only having them on for a few seconds and then ensuring an interval of at least a minute before they next light I intend to ensure this does not happen.

I have some electronic components to mix together to produce a circuit which will pulse a current through the cable, alternate the dvm between the near and far end of the cable and have a limitation on the minimum interval between pulses of current - I have in mind 60 seconds and 5 seconds for freddo to take the two readings. He will press a button and then one pulse of current will occur to take the voltage measurements; then a wait of 60 seconds before another pulse can happen.

In an experiment it is normal practice to repeat measurements in order to deal with the inevitable errors and noise present. If it was me I would repeat the testing ten times to see if the results were consistent.

Our Jack Russell puppy is being sick so I must stop now.
 

Reply to Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
519
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock