I had a problem a couple of days ago with my boiler shutting down due to too high temperature difference between the input and output, which transpired to be because the boiler had been wrongly wired.

I have two zones in my heating system, so as I understand it there should be 5 wires between the controller and the boiler - L, N & E plus two switched live. But there was only a 4-core cable so the boiler had been wired in a slightly different way to accommodate this. Interesting to speculate whether the cable would have been fitted by the plumbing or electrical contractor in a new-build house! Anyway, it is what it is - but practically impossible to rectify as the two ends are on different floors and not directly one above the other.

The gas engineer who came to check it out rewired in a different way but acknowledged that it's still not optimal. He speculated that I may be able to do something with a wireless connection between the boiler and controller. Any ideas about how to do that, and what I would need to buy?

Thanks
 
What system is it, S, Y or other.
 
Two zone values would rewire 5 core.
 
Two zone values would rewire 5 core.
With a permanent live at both ends but nothing in between for the 5th core, I'm hoping there's a way to use a wireless device to provide the connection. It's a bit of a lash-up but may be possible these days.
 
I have two zones in my heating system, so as I understand it there should be 5 wires between the controller and the boiler - L, N & E plus two switched live. But there was only a 4-core cable so the boiler had been wired in a slightly different way to accommodate this.

The number of zones is irrelevant, boilers will require either 4 core or 5 core depending on where the pump is located.

For a system boiler, or if the pump is located adjacent to the boiler, 4 core to the rest of the controls is sufficient.
If the pump is located with the valves etc then a 5 core is required to allow the boiler to control the pump.
 
The pump is near the valves - so 5 cores needed
 
So as I understand it, you have L, N, E and only one other core going to the boiler, but you need two because you have two control functions: demand signal from valves to boiler and the pump control from boiler to pump. The latter has been missing until now, and the lack of pump overrun has caused the flow temperature to go over limit. Your suggestion is to transmit one of those functions with a wireless link, and @davesparks suggestion is to relocate the pump adjacent to the boiler so that the pump can be wired directly to it.

If it were mine, I would make some kind of simple multiplexer device to enable both the demand and the pump control to be transmitted in opposite directions over the one available cable core. It would be an hour's work with a couple of relays, diodes and transistors, but I wonder whether such a thing exists commercially in an easy-to-integrate form, that would avoid having to rely on wireless?
 
If it were mine, I would make some kind of simple multiplexer device to enable both the demand and the pump control to be transmitted in opposite directions over the one available cable core. It would be an hour's work with a couple of relays, diodes and transistors, but I wonder whether such a thing exists commercially in an easy-to-integrate form, that would avoid having to rely on wireless?

If it were mine I'd probably use a delay-off timer to keep the pump going for the required time.

As far as I know the pump overrun on boilers is a simple time based thing and not actually based on temperature.
 
Assuming you have a permanent mains supply at the end remote from the boiler, you could use this:
 
If it were mine I'd probably use a delay-off timer to keep the pump going for the required time. As far as I know the pump overrun on boilers is a simple time based thing and not actually based on temperature.

That sounds like a simple and practical solution. In the past there have definitely been boilers with thermostatic control of pump overrun, via separate contacts on the stat. I've never had cause to investigate how it works on modern boilers, but perhaps it doesn't really matter, so long as the pump doesn't just stop the moment the burner goes out.

The Mainslink remote control solution looks like a neat, practical device too. If it can do 1km indoors (?!) it ought to be pretty reliable from one floor to the next unless your building is a mass of rebar.
 
Assuming you have a permanent mains supply at the end remote from the boiler, you could use this:
Are you selling these or something?
 
  • Funny
Reactions: Jim_e_Jib
Assuming you have a permanent mains supply at the end remote from the boiler, you could use this:

I'm beginning to think you are selling these Avo 😀
 
  • Funny
Reactions: Jim_e_Jib
  • Like
Reactions: DPG
As Lucien and davesparks say, it's not really important how long the pump runs after the boiler shuts down as long as it runs for long enough to remove the heat soak. A simple delay off timer would be an effective solution.
 
The Mainslink is exactly the solution that was described to me and I thought I was looking for.

But relocating the pump also seems to be a simple and elegant solution.

Thanks guys
 
  • Like
Reactions: DPG
Last edited:
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Baku, Azerbaijan
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Cable missing in central heating wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
naylorpd,
Last reply from
davesparks,
Replies
32
Views
4,204

Advert