Hi all, we first fixed a extension a couple of weeks ago and they were going to have a 10.5 kw convection oven so we ran a 10mm cable to it... we have gone back to second fix today but they are not having that oven anymore instead they are now having a 4.6kw oven so 20A, now the guy I was working with is saying that the cable is now too big and needs replacing, I might be wrong but am I right in thinking that we can just down rate the MCP and keep the 10mm cable? or does the cable need to be smaller?
thanks guys.
 
You are the Electrician mate, whats your take?
 
  • Like
Reactions: 1 person
the mcb is to protect the cable not the device, why do you think fan manufacturer's say it needs to be fed from a fused spur
 
Thanks guys thought I was right when you got another electrician saying something else you start to doubt yourself a little
 
In situations like this, always get them to justify/prove their case.
They'll soon crawl away! :-)
 
well he wanted to down grade it because this new oven was only going to pull 20A and we have10mm cable that's why I was having the argument that we can keep the cable and down rate to a 20A MCB
 
If using a cable that is too big was a problem then that 10mm would have been no good for the original appliance !
 
  • Like
Reactions: 3 people
the cable would have been too big for original appliance as you are probably allowing for diversity, if your allowing for diversity yes the calculation only comes to 20.68A or 25.68A If theres a socket, but personally I don't like using diversity for cookers as for peace of mind at Christmas when they are probably using all hobs and oven so I go to manufacturers spec which is 10.5kw so 45.6A and for the reference method how we installed it 10mm takes 45A, little bit more expensive yes but nice to know cable size takes total demand, im a young spark finished last year and as for me asking the question this was because another spark who is older than me so more experienced was arguing that cable was too big, where I said we can just change breaker so I guess him saying that baffled me a bit don't know why so sorry for stupid question
 
Rip out the cable and put a smaller one in.

Don't listen to any of the idiots above who think that you can chop and change the standard circuits in the OSG as they fancy.

How on earth do you think a 10mm cable will manage to carry 20A?
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable Size Advice
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
BES SPARK,
Last reply from
Lucien Nunes,
Replies
24
Views
2,662

Advert