As the title suggests I am doing an EICR for a commercial premises this morning.

I haven't looked at the job yet, it was a kind of "just come do what you need to do" job. It is an accountants which obviously means quite a few computers and I do believe they have a 3 phase supply but only uses 2 because the shop next door has the other (from what the client understands)

Now my question is because he has told me both CU's are 3036's... do I need to have the circuits RCD protected? I know he's happy to upgrade both units, I already suggested RCBO's and got the thumbs up but computers.... RCD's..... dont mix well as I'm aware?

I do believe that the computers are plugged into socket outlets and some of the cables are sunk into the wall so only trunking in certain places. But the office is fairly old

C2 on domestic for bathroom circuits and downstairs sockets but commercial downstairs sockets? Much more unlikely but potentially I suppose. Client is happy for RCBO's but can I fit them with computers say 8 computers per floor and 3 floors

Thanks for any assistance with this
 
If its a genuine server room you might find that there are racks and each rack has two power distribution units, fed from two different circuits connected via commando sockets (so your not talking normal sockets) , as an ex IT engineer if you want redundancy then all but the really low end servers have the option for two or more PSU's, some of the blade systems we used a lot had 6 power supplies and you could lose upto 4 of them depending on the number of servers...

Power supplies in servers because of the heat etc commonly caused tripping, just ask a big bank when I started as an IT engineer, there was a faulty PSU, to test the psu was faulty not the cable or PDU etc I connected a spare power cable from the other PDU and plugged it into the faulty PSU to confirm that the PSU was actually bad before ordering a new one.... Well you see what I had not seen was that the faulty PSU had shorted taking out the circuit breaker rendering one of the two PDU's with no power, not a problem the servers carried on with the other PDU, that was until I connected that to the bad PSU, a big flash and bang later I tripped the other circuit breaker to the other PDU and took down all the servers in the rack, they controlled hundreds of ATM machines which all temporarily went down... I learnt a lesson that day that I never forgot and thankfully after a quick reset of the breaker everything came back up..

Anyway my point is until you get there you wont know what you are dealing with..
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Commercial premesis, computers, RCD or not to RCD?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
NellyManjaro,
Last reply from
catdog1121,
Replies
17
Views
8,133

Advert

Back
Top