When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains isolator. Or do I need to 10point check the mains isolator and then another 10point check on the contactor before removing.
Many thanks
 
TL;DR
Contactor. Proving dead. Which points to check. 3 phase
Also, never take anyones word that it has been isolated. Always check for yourself. A lesson I learned the hard way many years ago :-(
 
Why does it sound like an exam question to me??

As above, if you’re likely to use a screwdriver on a terminal, use a tester first.

Energising coil may not be 230v, but still test.

Mark everything with tape if not already labelled…. As everything is more than likely all the same colour of cable.
 
Whats a 10 point check? how have i survived nearly 50 years in the industry without knowing this
 
Whats a 10 point check? how have i survived nearly 50 years in the industry without knowing this

The industry standard method of making sure something is dead. Basically test every combination of phases, neutral and earth.
 
The industry standard method of making sure something is dead. Basically test every combination of phases, neutral and earth.
Thanks for reply. I just wondered if I must test the part to be replaced even tho I have tested mains isolator. Thsnks
 
Thanks for reply. I just wondered if I must test the part to be replaced even tho I have tested mains isolator. Thsnks
If you don't check at the item being replaced how can you be certain that you have turned off - AND LOCKED OFF - the correct isolator ?
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
 
  • Agree
Reactions: pc1966
Whats a 10 point check? how have i survived nearly 50 years in the industry without knowing this
If you have N cables then you have (N * (N-1))/2 pairs to check to know all are safe w.r.t. each other. So for:
  • Single phase (L + N + E) = 3 it is (3*2)/2 = 3 checks
  • 3-phase without N (just L1-3 + E) = 4 it is (4*3)/2 = 6 checks
  • 3-phase normal (L1-3 + N + E) = 5 it is (5*4)/2 = 10 checks
 
Last edited:
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Absolutely, the contactor control could be from a totally separate supply, maybe even UPS-backed!
 
  • Like
Reactions: DefyG
Mark everything with tape if not already labelled…. As everything is more than likely all the same colour of cable.
Also take photos before and after, handy for any reports or problems that might have occurred.
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Brill thanks. If I was to double check at the contactor. Would you do the 10 checks again or just check the between the phases. Thanks
 
Brill thanks. If I was to double check at the contactor. Would you do the 10 checks again or just check the between the phases. Thanks
If a 3P contactor just 6 checks per side, the 3*L and the CPC/chassis.
 
  • Like
Reactions: 3phase and DefyG
If a 3P contactor just 6 checks per side, the 3*L and the CPC/chassis.
Also check coil terminals A1 A2 as could be from different source.
 
Thanks for all your help. Totally makes sense now
 
  • Like
Reactions: pc1966 and DPG
If you have N cables then you have (N * (N-1))/2 pairs to check to know all are safe w.r.t. each other. So for:
  • Single phase (L + N + E) = 3 it is (3*2)/2 = 3 checks
  • 3-phase without N (just L1-3 + E) = 4 it is (4*3)/2 = 6 checks
  • 3-phase normal (L1-3 + N + E) = 5 it is (5*4)/2 = 10 checks
Thanks pc1966, never heard it called that before.
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Contactor. Proving dead . 3 phase .
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
3phase,
Last reply from
R-fur,
Replies
16
Views
2,387

Advert