Just wondering what you guys generally do to determine the EFLI of a circuit during testing. Do you calculate it, as in Zs=Ze+(r1+r2), or do you measure for each circuit, or both. I tend to calculate it these days, simply as it's quicker, but just wondered what others do.
 
Usually with RFCs I just stick the megger in and let it do all the hard work, then for anything such as lighting, boiler etc where it'd be considered working live/near live parts (Naughty) I calculate but put a little * on the cert with a note at the bottom noting calculated values
 
... then for anything such as lighting, boiler etc where it'd be considered working live/near live parts (Naughty) I calculate but put a little * on the cert with a note at the bottom noting calculated values

Not naughty at all. How do you get your Ze then? By enquiry? :laugh3:

Measure every time for me. It's a good check that everything's been re-connected as it should be, especially if you do a Z l-n at the same time to check the neutral.
 
  • Like
Reactions: 2 people
Both. Calculate first to give worst case scenario (before parallel paths) and enter on cert then measure last point on each circuit at the end to make sure this is less than or equal to the calculated value and that everything has been reconnected properly
 
It is all well and good calculating it, but it doesn't prove that you have an earth, testing it does. I know calculation is acceptable, but measurement is better if you think about it, and although Ze =Zs +(R1+R2], a measured result will always be a bit lower (or should be) due to parallel paths, and the current that the tester is forcing around the circuit.

Cheers……………..Howard
 
  • Like
Reactions: 1 person
It is all well and good calculating it, but it doesn't prove that you have an earth, testing it does. I know calculation is acceptable, but measurement is better if you think about it, and although Ze =Zs +(R1+R2], a measured result will always be a bit lower (or should be) due to parallel paths, and the current that the tester is forcing around the circuit.

Cheers……………..Howard

And that's why it's better to calculate.

Parallel paths come and go, and you have already proven you have an earth so I don't agree with you at all.
 
calm down, calm down.....

scousers.jpeg
 
  • Like
Reactions: 1 person
Measure.

It is possible that your low current Continuity tester will indicate a sound connection, whilst the high current Loop Impedance tester will expose a possible weakness.

Regards

Billy
 
If you've proven continuity and measured your Ze, then calculating Zs is fine by me. But it actually doesn't take that long to measure, so I suppose you just get better piece of mind by doing so.
 
We discussed this a day or two ago and decided to verify the circuit a measured ZS was needed, can't remember which thread it was now but it made sense afetr reading it all.
 
And that's why it's better to calculate.

Parallel paths come and go, and you have already proven you have an earth so I don't agree with you at all.

I do agree with this reasoning, and as a rule I tend to calculate. If there's a lot involved with disconnections for measuring, however, I'll happily measure.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
EFLI - measure or calculate?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
33

Thread Tags

Advert

Thread statistics

Created
kingeri,
Last reply from
Lucien Nunes,
Replies
33
Views
6,343

Advert