Discuss EFLI - measure or calculate? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

kingeri

-
Esteemed
Arms
Reaction score
1,345
Just wondering what you guys generally do to determine the EFLI of a circuit during testing. Do you calculate it, as in Zs=Ze+(r1+r2), or do you measure for each circuit, or both. I tend to calculate it these days, simply as it's quicker, but just wondered what others do.
 
Usually with RFCs I just stick the megger in and let it do all the hard work, then for anything such as lighting, boiler etc where it'd be considered working live/near live parts (Naughty) I calculate but put a little * on the cert with a note at the bottom noting calculated values
 
... then for anything such as lighting, boiler etc where it'd be considered working live/near live parts (Naughty) I calculate but put a little * on the cert with a note at the bottom noting calculated values

Not naughty at all. How do you get your Ze then? By enquiry? :laugh3:

Measure every time for me. It's a good check that everything's been re-connected as it should be, especially if you do a Z l-n at the same time to check the neutral.
 
Both. Calculate first to give worst case scenario (before parallel paths) and enter on cert then measure last point on each circuit at the end to make sure this is less than or equal to the calculated value and that everything has been reconnected properly
 
It is all well and good calculating it, but it doesn't prove that you have an earth, testing it does. I know calculation is acceptable, but measurement is better if you think about it, and although Ze =Zs +(R1+R2], a measured result will always be a bit lower (or should be) due to parallel paths, and the current that the tester is forcing around the circuit.

Cheers……………..Howard
 
It is all well and good calculating it, but it doesn't prove that you have an earth, testing it does. I know calculation is acceptable, but measurement is better if you think about it, and although Ze =Zs +(R1+R2], a measured result will always be a bit lower (or should be) due to parallel paths, and the current that the tester is forcing around the circuit.

Cheers……………..Howard

And that's why it's better to calculate.

Parallel paths come and go, and you have already proven you have an earth so I don't agree with you at all.
 
If you've proven continuity and measured your Ze, then calculating Zs is fine by me. But it actually doesn't take that long to measure, so I suppose you just get better piece of mind by doing so.
 
We discussed this a day or two ago and decided to verify the circuit a measured ZS was needed, can't remember which thread it was now but it made sense afetr reading it all.
 
And that's why it's better to calculate.

Parallel paths come and go, and you have already proven you have an earth so I don't agree with you at all.

I do agree with this reasoning, and as a rule I tend to calculate. If there's a lot involved with disconnections for measuring, however, I'll happily measure.
 

Reply to EFLI - measure or calculate? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
715
Assuming that you measure the windings for a power transformer, for example: A-B: 2,258 ohms B-C: 2,262 ohms A-C: 2,250 ohms, how do you...
Replies
1
Views
552
Hi All, Any help would be greatly appreciated. When calculating the Zs for a circuit specifically for 2396 do you have to incorporate the on site...
Replies
0
Views
474
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
791

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock