Garage consumer unit rcd trips out

Discuss Garage consumer unit rcd trips out in the Lighting Forum area at ElectriciansForums.net

thanks for the replies so far. yes lol am in redcar . near race course lol

have replaced the switch at front of garage . i check loose connections on the two light fittings.
any good sparkeys in this area ??

got to be a fault on the two light flourecents ?? evidence seems to be going that way and all saying on here and elsewhere flourcents suck.
have checked connections already on garage consumer unit and all are good.

if i switch one or both of the suspect lights off on average it will trip the rcd 3 out of 10 times , so its a annoying fault. its on this cicuit as it doesnt do it now since temp fitting two light pendants with 60 watt bulbs in. which goes back to original comments made by people on here and elsewhere its the ballast on the flourecents discharging on switch off?? thanks all for your help so far , very much appreciated and listened too.
 
Try what SparkyChick suggests first.I think you might find that's the problem especially with you saying that you could hear crackling.Also check the busbar under the breakers.(After isolating the unit!). I use my mobile phone camera to look along the breakers and make sure each one is clamped onto the busbar.It's amazing how many times the breaker connection has missed the busbar and is just touching it instead.
you posh git. i use a candle and a mirror.
 
thanks for the replies so far. yes lol am in redcar . near race course lol

have replaced the switch at front of garage . i check loose connections on the two light fittings.
any good sparkeys in this area ??

got to be a fault on the two light flourecents ?? evidence seems to be going that way and all saying on here and elsewhere flourcents suck.
have checked connections already on garage consumer unit and all are good.

if i switch one or both of the suspect lights off on average it will trip the rcd 3 out of 10 times , so its a annoying fault. its on this cicuit as it doesnt do it now since temp fitting two light pendants with 60 watt bulbs in. which goes back to original comments made by people on here and elsewhere its the ballast on the flourecents discharging on switch off?? thanks all for your help so far , very much appreciated and listened too.
thanks for the replies so far. yes lol am in redcar . near race course lol

have replaced the switch at front of garage . i check loose connections on the two light fittings.
any good sparkeys in this area ??

got to be a fault on the two light flourecents ?? evidence seems to be going that way and all saying on here and elsewhere flourcents suck.
have checked connections already on garage consumer unit and all are good.

if i switch one or both of the suspect lights off on average it will trip the rcd 3 out of 10 times , so its a annoying fault. its on this cicuit as it doesnt do it now since temp fitting two light pendants with 60 watt bulbs in. which goes back to original comments made by people on here and elsewhere its the ballast on the flourecents discharging on switch off?? thanks all for your help so far , very much appreciated and listened too.
 
whats the best make on the market at the minute for 6 feet led battens for quality and reliability ? I post thus question on a new thread as well. As worse case scenario here for me is i up date these flourecents to led specification and the fault is still there .but i be saving and improving the lights in the long run regardless of whether i get a electrician out to have a look or not if fitting led battens doesn't fix the issue.

Are knightbridge a good make??
 
Hi,have you watched the episode of "Father Ted",where Ted is explaining to Dougal,that "these" are models,and "those" are far away...?

If you are continually adding and altering an already faulty set-up,you will be complicating any testing which will be required,to find your fault(s). :)
 
whats the best make on the market at the minute for 6 feet led battens for quality and reliability ? I post thus question on a new thread as well. As worse case scenario here for me is i up date these flourecents to led specification and the fault is still there .but i be saving and improving the lights in the long run regardless of whether i get a electrician out to have a look or not if fitting led battens doesn't fix the issue.

Are knightbridge a good make??
That is a bit of a hard question as even the so called premium brands are buying the leds inside off the open market and a lot of the lights regardless of brand and packaging are made by a handful of companies with pretty much identical parts. I have fitted numerous LAP led battens from screwfix and had no issue. quick and easy to install with screwless connections inside.. its about the only good thing in the LAP range mind!
 
before i replace what i believe to be the failing flourecents causing the rcd to trip i am going to swap around two of the four lights that are working to the circuit with the suspect flourecents on . if they work on this circuit i will know they are faulty and will replace with led versions instead . as it wont be any think that has failed if this test works. as the circuit works with normal pendant light with 60 watt bulbs in no issues. so i dont think it wiring fault .
if this test fails i am going to get a electrician in to test the circuit and measure resistance etc as done all i can as a home owner to find this fault without causing any harm.
 
Last edited:
Just make sure you follow a safe isolation procedure. Can't recall, did you check for loose connections & replace both two way switches?
 
have checked for loose connections in light fittings and inside garage consumer unit .
have replaced the switch at the front of the garage as i could hear it arching when i use it to switch the lights off.
not changed the switch at the back of the garage as one side on each switch is wired to a different light . and is working ok with light pendants .
yes i will switch off the main breaker switch as well as the mcb to isolate rather than light circuit mcb on its own to be on the safe side .

if this test still causes the rcd to trip then it wont be the flourecents i think , but i get a electrician in then as can do no more . the only conclusion could be made if its does trip when i swap over the light fittings is the circuit could be wrong but i aint going any further and i will get some one in ......
 
If those luminaires causing the issue are on a two way switching, it would be a good idea to replace both switches, to eliminate that possibility.
 
If those luminaires causing the issue are on a two way switching, it would be a good idea to replace both switches, to eliminate that possibility.
You need to involve an Electrician to test the faulty circuit, replacing accessories willy nilly is not the way forward.
 
You need to involve an Electrician to test the faulty circuit, replacing accessories willy nilly is not the way forward.

I disagree. Checking for loose connections, checking switches would seem a simple check, before replacing luminaires as others have suggested. As long as the OP feels confident to do so.
 
I disagree. Checking for loose connections, checking switches would seem a simple check, before replacing luminaires as others have suggested. As long as the OP feels confident to do so.
If you feel happy with your suggestion, then run with it Middy, me I try not to offer advice to DIYers could be dangerouse.
 
I disagree. Checking for loose connections, checking switches would seem a simple check, before replacing luminaires as others have suggested. As long as the OP feels confident to do so.
If you feel happy with your suggestion, then run with it Middy, me I try not to offer advice to DIYers could be dangerouse.
 
If you feel happy with your suggestion, then run with it Middy, me I try not to offer advice to DIYers could be dangerouse.

Not sure why you are singling me out for this guidance; other members have advised the OP to replace the luminaires, check for loose connections or incorrectly installed mcb's. Why don't you give them such council?
 
Not sure why you are singling me out for this guidance; other members have advised the OP to replace the luminaires, check for loose connections or incorrectly installed mcb's. Why don't you give them such council?
Not singling you out Mate just answering your post.
 
Not singling you out Mate just answering your post.
Sorry for the abrupt response Middy I was only answering your post, there was not an intention of singling you out, as there was no need to, my quick reply was due to her indoors calling me for tea is ready, and it was Chilli and that is not to be missed
 
Sorry for the abrupt response Middy I was only answering your post, there was not an intention of singling you out, as there was no need to, my quick reply was due to her indoors calling me for tea is ready, and it was Chilli and that is not to be missed
 
Finding the fault rather than replacing everything until the RCD doesn't trip is a far better way forward. The fault could be a damaged cable so changing all switches and fittings could achieve nothing
 
Well swapped flourecent over to what i know are good units
Still the same result . Rcd trips whilst switching one of the units off.

This now narrows it down for and confirms the following :

The flourecents units work fine as taken them from a different circuit .
The switches are fine as i have fitted light pendants to the circuit that i know is at fault in replacement to the flourecent and they work fine from both ends of the garage.

The fault for me it carnt be a break in the wiring as the pendants worked fine.

As i said before its when you switch the flourecents on and off after about 4 times it trips the rcd out.

For me the issue is inside the garage consumer unit as it carnt be any where else as i have proven this by doing the above.

I think it has got to be some back serge in electric when i switch the flourecent off its got no where to go but to trip the rcd but its only on one light circuit the other light cicuits which i switch on the four other lights individualy doesnt trip the rcd.

Is it because its switched from both ends and the way the wiring has been done in the fuse box.
I can go no further with this as i think there will be little point in getting a larger rcd unit as that wont achieve any thing.

Unless this unit is reaching its upper limit off resistance with these flourecents and putting a bigger unit in will resolve the issue.

For me i think now i need to get some one in.

I was just checking altogether on one mcb i have 6 6 feet flourecents and 2 x 3 feet units on the side wall

I have on the outside of the garage to pir coach lamps and on the back of the garage a spot light but they are on a different mcb so doubt will cause the rcb to be at it maximum?

Thing is it goes off in the daytime so these light wont be switching on in any case.

Time out i think i give up . I get it tested now....
 
Last edited:
It is something to do with a two way switching circuit and these flourecents with this rcd. Carnt be any thing else.

Light pendants work on this two way circuit.
Two flourecent dont. Took flourecents from another part of ceiling of garage and made no difference. Still trips rcd
 
Can i just ask you guys this question.
When i got the garage consumer unit fitted and tested by the electrician could he have mis wired this circuit?

What i mean is could he have wired this circuit in to another part of the garage consumer unit by mistake such as the sockets circuit and this might be whats causing the rcd to trip out as its over loading on this one circuit? However i know he has tested the system and took readings as i still have the certificate.
Just a thought. ..
 
This is what happens when Kev the kitchen fitter rewires your garage:

Lime.jpg

For the record he's used 0.75mm flex for the socket circuit!
 
Reading only the opening post
The description of how its tripping,the very hasty conclusion that the operation of loading to one particular circuit was tallying with the tripping Rcd
Therefore it "must be" the offending (in this case fluorescent fitting) causing the problem

That is a wrong conclusion for you to make
It is not the way to identify a problem or problems, it certainly does not confirm any such thing as a cause ( which was claimed in the first post)
You are probably,not possibly,probably, being sidetracked to the real cause by incorrect assumptions
 

Reply to Garage consumer unit rcd trips out in the Lighting Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock