My exam is coming soon and I have a question.
My installation is single phase , TN-S. There is a shower unit protected by the RCD. My questions are:
Do I carry out RCD test at the RCD itself in the C/U or do it at the shower unit itself? If at the shower unit where does the tests leads go?

Many Thanks.
 
Which exam are you on about out of interest?
 
Ah, ok. You can carry out the test at the CU. Line lead to 'line out' on RCD (bottom left), neutral lead to 'neutral out' on RCD (bottom right) and earth lead to earth bar.

Edit: Presuming that it's a normal RCD :D
 
So there is no need to do RCD test on the shower unit itself? Yes the RCD is normal.

Many thanks.
 
No, the clue is in the title :)

It's called an RCD test, not a shower and RCD test.

Happy to help :)
 
  • Like
Reactions: 2 people
what about an RCD trip time test, that would have to be done at the shower isolator no
 
To complete the picture you're testing the RCD only with this test (that's why it's with loads disconnected, so you can be sure that only the trip current from the meter is being used to trigger the RCD). The Zs (in combination with the other tests) of all the other circuits being within spec is sufficient proof that the RCD will work for the circuits routed through it.
 
  • Like
Reactions: 1 person
ok, but why then is the RCD trip results on an EIC on every circuit, why not just have one box for the entire cert, or 2 boxes x1 & x5
 
ok, but why then is the RCD trip results on an EIC on every circuit, why not just have one box for the entire cert, or 2 boxes x1 & x5
A good question, I'll pass on that one, that's a question for the form designer.

For an RCD (as opposed to RCBO) I use two separate lines on the form and record the times for x1 x5 at both 0 and 180 for posterity (one line for 0deg and one for 180deg).

If you did test the RCD from each circuit, you would actually get slightly different timings for each point/circuit tested (because of the EFLI from that point on the circuit being different for a radial for example).

The maximum Zs values have been worked out to ensure that sufficient fault current can flow to cause the device to trip. You can see the advantage, it's easier to do at the CU; you need to reset the RCD for each test (5 tests, 4 trips, 5 resets). The more modern tests have an auto mode making it even easier. Imagine the situation if you were trying to test the upstairs lighting circuit. You'd be up and down stairs a lot if working alone on it.

It will be the same if you are ever asked to "ramp test" an RCD or RCBO, you do it at the device. HTH.
 
As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.
 
  • Like
Reactions: 3 people
For dual RCD boards, usually on the EIC or whatever, I usually just fill in one row for the first RCD and then all of the circuits for that side of the board underneath, then the second RCD with all of that sides circuits underneath.

As Biff said, the worst case (longest trip times) for both.
On the 17th Amd.1 sheets, they now have spaces for Idn and 5X Idn.

Obviously for RCBO's seperate times, one for each circuit using RCBO's
 
  • Like
Reactions: 1 person
As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.
Yep, that's all that's required (and I don't do that for RCBO's, only for RCD's covering more than one circuit).
 
As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.

In fact i can remember a former supervisor insisting we write both 0 & 180 times in the tiny winy microscopic NIC cert boxes.
What a dick lol.
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How to carry out RCD test for shower?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
nazoom,
Last reply from
IQ Electrical,
Replies
29
Views
5,805

Advert