Hi,

Apologies for the basic (silly!) question, but using a maintenance free box (ashley j803) to extend a ring main circuit, in the configuration in the image attached with 4 cables (2 in, 2 out), would it not create issues having the separate 2 cables in and out, in contact with each other? Should they not be connected separately (2 junction boxes) or is everything connected to each other in the end and it doesn't matter?

Cheers!

J803.jpg
 
This would be known as a 'figure of eight' RFC, is not permitted, and there is a specific test prescribed in the regs. to root any such arrangements out.
Either 6 pole j/box, or two separate 3 pole is required.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Junction Box Question
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
wassupjg,
Last reply from
brianmoooore,
Replies
1
Views
1,245

Advert