neutrals at switches

Discuss neutrals at switches in the Australia area at ElectriciansForums.net

W

wattsup

easy peasy wiring....i never used to do it, but now seems common practice...I was intending to use dp grid switches...but now ahhh, we want dimmers . No probs with the rotary dimmers but a neutral connected in the backbox. Is that bad pactice?
 
I dislike doing that in domestic properties because i don't trust some householder not to come along and 'convert' it into a socket to run their vacuum cleaner off.
Otherwise it's perfectly acceptable (easier for downlighers) and you don't even need DP switches - you can use a bit of terminal block behind the switch because the joint is accessible.
 
Hi Wattsup,

It used to be considered bad practice but is now acccepted. If the neutrals are clearly identified by colour and installed as per BS7671 etc I don't think there is an issue. It is taught in colleges as an option to 'take the power to the switch'as well as to the ceiling rose. I agree with NovusSparkus that the DIYer will or can do conversions but surely the comeback would be with them if the installation complied? We can't prevent such changes and provided the installation was correctly documented and legal then the law should protet the electrician.

Hope this helps,

Best wishes

Rex
 
Yep do it most of the time, much easier...

you can use a bit of terminal block behind the switch
you can also use one of these, which are very good quality, quick and simple to use:

Verbindungskl2-g.jpg
 
It,s been common place for years in the commercial world,especially on a conduit install. In the domestic world I am not convinced that this should become the norm over 3 plate. Just an opinion I know. And why the need for neutrals at the switch, just because a dimmer is involved ? There are so many line and load only dimmers on the market.
 
easy peasy wiring....i never used to do it, but now seems common practice...I was intending to use dp grid switches...but now ahhh, we want dimmers . No probs with the rotary dimmers but a neutral connected in the backbox. Is that bad pactice?

on a tech note it helps to cancel out emf running them together you can see it happening with tv's sometimes when you get flux on the picture. Really helps those with hearing aids thats why on 3plate you wire induction loops on two ways.
 
Another consideration should be given to the fact that for a number of reasons it can be an advantage having a permanent live at the fittings ie ext fans, smoke detectors, even a possible e/m light fitting. all possibles at a future date, with 3 plate. Also whilst it may simplify connections at the light fittings,to have neutrals at the switch, it will complicate things at the switch positions. I would only do this if neccassary, again just an opinion. Also any inductive/back emf sensitive equipment should be run in screened or shielded cables to be on the safe side anyway's. Again just an observation, we all have our prefferances.;)
 
I think it is great to just have the one cable at the light and like to do it where i can when I know fancy lights are being used.
I hate chasing though so I wouldn't bother to do it on a rewire if I could pull one cable down to the switch but not three.
 
And why the need for neutrals at the switch, just because a dimmer is involved ?

no need, as i said i was going to use dp switches, then the customer later decides on dimmer switches, so i'm stuck wiith neutrals in a connector, at that particular switch.

the reason I was using dp switches was simply for my own get out of jail card...what neutrals at switches!...err yes but dp switches. In the commercial / industrial world it is unheard of, all singles in conduit, trunking is the norm.
 
Another consideration should be given to the fact that for a number of reasons it can be an advantage having a permanent live at the fittings ie ext fans, smoke detectors, even a possible e/m light fitting. all possibles at a future date, with 3 plate. Also whilst it may simplify connections at the light fittings,to have neutrals at the switch, it will complicate things at the switch positions. I would only do this if neccassary, again just an opinion. Also any inductive/back emf sensitive equipment should be run in screened or shielded cables to be on the safe side anyway's. Again just an observation, we all have our prefferances.;)
Not to start a fuss but what about isolation for e/m and smokes. Your still going to have to knock out for a test switch.
 
It would be mighty congested if you had a two gang two way switch with neutrals at the switch.

Agree competely Ian.
I think there is a place for both methods, but using the neutral at switch as a preferance over 3 plate on a regular basis would not be a good thing. 3 plate in domestic installs is well proven, yes there are examples when the latter may prove beneficial but not as a replacement to tried and tested methods. If its not broke, why fix it.;)
 
Agree competely Ian.
I think there is a place for both methods, but using the neutral at switch as a preferance over 3 plate on a regular basis would not be a good thing. 3 plate in domestic installs is well proven, yes there are examples when the latter may prove beneficial but not as a replacement to tried and tested methods. If its not broke, why fix it.;)
you have to isolate the circuit with 3-plate to change fitting

also light fitting is congested with wires
 
loop out ceiling is ok when one fitting, but 12 lights switched 2-gang is a semi-problem (not problem really but hassle). It is easier to first fix loop in ceiling, but much harder 2nd fix.

If it were a new build, i would use singles all the time
 
It would be mighty congested if you had a two gang two way switch with neutrals at the switch.

Which is exactly what i have, which is why i have been reading this forum. 2x supply 2 core an earth (one in, one out to next room) 2x 3core an earth, 2x 2core an earth to lights. I can get rid of one supply cable by moviing it to the last room on that particular circuit but that still leaves me with5 cables in one switch box ie 17 individual cores. my initial thought was oh s..t, but now i'm thinking shall i just make the box deeper ( a lot deeper ). I am fitting 14 downlighters split on the two circuits. Any thoughts !!!
 
Haven't got BGB to hand, but I believe that 2011 now says that consideration should be given to provide a neutral at a switch position. The intent behind this is for electronic switching devices that require one.
 

Reply to neutrals at switches in the Australia area at ElectriciansForums.net