They probably did not mention the neutral to earth fault as the schdule does not have a box for N/E insulation test results.
Wonder why the shower is on a 5 sec dis ?
Type (Type )MCB s theses must be new!

On a serious note putting the up sockets on the non RCD side of the board is unaccepable and fobbing you off saying badly wired plug ,they new the fault was there when or if they tested (might of been RCD not holding test when energised) as all plugs etc should of been removed for testing!

Cash in hand or whatever method of payment the elctrician has changed the CU and has to do this as per the current regulations!

A few tests prior to the CU being changed would of identified any IR problems and I wonder if the house has a borrowed neutral what with both lighting ccts on the same RCD.

A picture of the inside of the consumer unit would be good!

I do hope this issue is resolved sooner rather than later let us know!
 
@mhar - When filling out test sheets, it asks for the max permitted value as stated by the BS7671 not the adjusted value for temp' compensation that the onsite guide gives you.
 
@mhar - When filling out test sheets, it asks for the max permitted value as stated by the BS7671 not the adjusted value for temp' compensation that the onsite guide gives you.
Hi DW and MHAR - These days I put a clarifying comment in case Inspector Clouseau wants to look. Hopefully readers are aware of the need for the 2 values. ;)
Cheeky Comment : As the OSG values seem calculated by applying BYB Appendix 14 to Table 41.3, l guess you could say it was the max value from BYB ?
 
The fact that the test results bear almost no relation to what is installed and written on the consumer unit is very suspicious.

The fact there is a neutral-earth fault on the upstairs sockets may mean that any leakage could be passing through the earth bar of the consumer unit and then passing along the bonding cable and onto the gas pipe. We don't know if the consumer unit is properly earthed do we?

I hope this gets sorted :)
 
Last edited:

Reply to New kitchen, live earth fault!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
951
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
545
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
933
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock