They probably did not mention the neutral to earth fault as the schdule does not have a box for N/E insulation test results.
Wonder why the shower is on a 5 sec dis ?
Type (Type )MCB s theses must be new!
On a serious note putting the up sockets on the non RCD side of the board is unaccepable and fobbing you off saying badly wired plug ,they new the fault was there when or if they tested (might of been RCD not holding test when energised) as all plugs etc should of been removed for testing!
Cash in hand or whatever method of payment the elctrician has changed the CU and has to do this as per the current regulations!
A few tests prior to the CU being changed would of identified any IR problems and I wonder if the house has a borrowed neutral what with both lighting ccts on the same RCD.
A picture of the inside of the consumer unit would be good!
I do hope this issue is resolved sooner rather than later let us know!
Wonder why the shower is on a 5 sec dis ?
Type (Type )MCB s theses must be new!
On a serious note putting the up sockets on the non RCD side of the board is unaccepable and fobbing you off saying badly wired plug ,they new the fault was there when or if they tested (might of been RCD not holding test when energised) as all plugs etc should of been removed for testing!
Cash in hand or whatever method of payment the elctrician has changed the CU and has to do this as per the current regulations!
A few tests prior to the CU being changed would of identified any IR problems and I wonder if the house has a borrowed neutral what with both lighting ccts on the same RCD.
A picture of the inside of the consumer unit would be good!
I do hope this issue is resolved sooner rather than later let us know!