Hi guys new to the forum after bit of advice. My family are installing a new shed in the garden and require a lot of power ie few sockets, lights. I am planning of running a swa fed from 32a mcb from the main board to a sub board.
Have a question-
Shall I install the new 32a mcb in the main board on the RCD side or main switch side?
Thanks
 
I agree with above but as a general rule it is better to use a cable which omits RCD protection on the distribution side. Just think if something trips in the shed it’s going to take all of the other RCD protected circuits out along with it. Install RCD protection in the shed to cover final circuits.
 
are you planning to earth the swa armor and if so what is the design earth loop impedence via the armor at the far end? also what Type is the MCB you are planning to use?
 
You should always earth the Armour
I was not suggesting that they shouldn't, but I'm sure there's a lot of SWA with no earth on the armour.
You wouldn't get any of the benefits of SWA but you'd still get the cost, so it'd be pointless to install RCD protected SWA where normal multi core cable would be allowed.
 
Thanks for the replies guys, I was planning on using swa because because it's going to be run external but clip direct not buried at any point.
I did think RCD only at the sub board would be the best setup.
Earthing arrangement is TN-CS
Now the issue with earthing the armour is the main board is plastic so the 'o ring' would be useless but it will be done on the new sub board. Earthing will be identified using the black core both ends.
 
I might be wrong but im assuming the op is not an electrician as some of his replies are lacking even basic knowledge.
I am surprised the thread is open still as i can see it turning into us designing the whole job.
No mention of how he is getting this signed of by an electrician of bc to comply with part p either
 
Im still in training at the moment this is all new to me, my family will be getting in a local spark but im intrigued to learn the installation method. Thanks for the comments
 
New posts

Reply to New sub board for shed swa advice. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock