Hi All,

absolutely aware of my own limitations as a diy' er and limit myself to replacing fittings rather than new installations.

Replaced 4 x 240v GU10 downlighters in the bathroom(ceiling 3m high) and when I turn the light switch on , the MCB trips all lights in the flat. before I replaced the fittings, I never had an issue.

1 gang light switch feeds a 1mm cable up to the ceiling and lights are connected in series, used new cable, connecting all the lives together, all the nuetrals together and earths together.

Have I missed something?
 
  • Funny
Reactions: johnduffell
A very common and dangerous mistake, my money is on one of those neutrals being a switch live, if this is within your limit as you say do your have the correct equipment to test for this?
Also a bathroom is a special location.
 
Last edited by a moderator:
Apologies just re-read your post which says that it’s switched fed so you have a neutral at the switch
 
1 gang light switch feeds a 1mm cable up to the ceiling and lights are connected in series, used new cable, connecting all the lives together, all the nuetrals together and earths together.

Have I missed something?

That is NOT in series then, it is in parallel (which is correct).
 
You'll just have to double check each connection and if that doesn't find a problem, employ an electrician with suitable fault finding equipment.

Are you central Edinburgh? kind of out of my way but nice drive up the coast
 
Apologies just re-read your post which says that it’s switched fed so you have a neutral at the switch
I think you were correct in the first place.
 
  • Agree
Reactions: johnduffell
Could you drop the lights and take some pictures? It may help to identify anything you may have missed. When you say the "...MCB trips..." do you mean the MCB or RCD, you do have RCD protection?
 
Classic lighting error, as above one of the blues must have been missing a brown sleeve as it's a switched live. Are the lights on when the switch is off?
Do you have the before and after photos of the wiring?
 
  • Optimistic
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
Freddie,
Last reply from
johnduffell,
Replies
8
Views
929

Advert