Hi, i'm currently doing my Level 3 design project and it's going to be tricky with the coronavirus and lack of contact with Tutor and other students.

Its the Hotel Swimming pool one

and I have to select luminaries for the cafe pool.

I haven't chosen my luminaries but I'm thinking to do it all with SELV 12V now how do I do cable calculations and Max Demand for a Selv circuit? Also what cable should I use, I was thinking FP200 as it's a public area is this ok for Selv?

You may laugh at my suggestion but any help would be great.
 
We have a trainee only area... you should contact @Dan or @Lou to get access to it. Things like this are covered in there much more than in the public area.
 
  • Like
Reactions: Lister1987
Upvote 0
We have a trainee only area... you should contact @Dan or @Lou to get access to it. Things like this are covered in there much more than in the public area.
Ok thanks, ill give it a go.
 
Upvote 0
In the meantime however... what's the basis for your choice of SELV?
 
Upvote 0
In the meantime however... what's the basis for your choice of SELV?
Logically it would make sense, why run 240v when 12v will be inherently safer and do the same job, you can get presentation converters to change ES type bulb holders to take 12v bulbs
 
Upvote 0
Maximum demand and cable calculations are the same for SELV as they are for LV, however voltage drop plays a much bigger role, and is far more noticeable if you get it wrong.

I don't understand your statement that you think it should be FP200 because it is a public area.
FP200 is a fire performance cable designed to be used for circuits which need to continue to operate when exposed to fire, different grades being available for different fire performance requirements (FP200 gold, FP200 enhanced). FP200 is usually not an ideal choice for general wiring applications as it doesn't have the same mechanical strength as the other options plus it is more expensive than the alternatives.

Being in a public area, or public building suggest you should be using a cable with LSF insulation(and sheath if sheathed).
When chossing the type of cable you need to consider things like the potential for mechanical damage, installation method, ease of future alteration, environmental factors, price, fitting in with the design/aesthetic of the building.
[automerge]1585151625[/automerge]
Logically it would make sense, why run 240v when 12v will be inherently safer and do the same job, you can get presentation converters to change ES type bulb holders to take 12v bulbs

As the voltage is lowered the cable size goes up dramatically, this is why we don't run everything at a safer, lower voltage.

Why would you need to convert ES lampholders to another type on a 12V system?
 
  • Like
Reactions: DPG and SparkyChick
Upvote 0
Thanks for the reply's the questions are
here HELP PLEASE!!! 2365/615 electrical system designs - https://www.electriciansforums.net/threads/help-please-2365-615-electrical-system-designs.169479/#lg=attachment45404&slide=0

Basically I would like to get started and do some calcs etc but I can't even find suitable lights

Ideally if I was doing this for real I would like to use Selv max of 50v and LSF cable - I think FB200 is LSF

but I can't find any kind of Selv light that would be suitable for this setup also can't find any info for calcs on voltage drop of a Selv cable.

I suppose I can just use some normal high IP lights as there on the ceiling.

but any advice would be great :)
 
Upvote 0
Are these lights actually submerged in the pool if not do they fall within any of the zones.
 
Upvote 0
Upvote 0
SELV should be avoided unless absolutely necessary. Do they fall within one of the zones. Is it actually in the vicinity of the pool or a separate room.
 
Upvote 0
You need to read the assignment properly Mark & not make it complicated becuase your tutor will just hand it back to you & ask why. You dont need Selv for the pool area or nothing like LSF cable.
Make it simple
 
Upvote 0
SELV should be avoided unless absolutely necessary. Do they fall within one of the zones. Is it actually in the vicinity of the pool or a separate room.
The drawings are here in PDF

The ceiling directly above the pool what Zone would that be? 2 I think its ok.
 
Upvote 0
Doesnt matter Mark what Zone it is above the Pool as you're not going to put lights there. You just need wall lights & non-maintained emergency lights on the walls.
 
Upvote 0
Wall lights would be Zone 2 and wouldn't be very good.
 
Upvote 0
Wall lights would be Zone 2 and wouldn't be very good.

This is where you would use your assumptions regarding height of walls where to fit etc
 
Upvote 0
After further looking Zone 2 only needs Selv if it is not protected by a RCD can anyone confirm this?
 
Upvote 0
Thanks for the reply's the questions are
here HELP PLEASE!!! 2365/615 electrical system designs - https://www.electriciansforums.net/threads/help-please-2365-615-electrical-system-designs.169479/#lg=attachment45404&slide=0

Basically I would like to get started and do some calcs etc but I can't even find suitable lights

Ideally if I was doing this for real I would like to use Selv max of 50v and LSF cable - I think FB200 is LSF

but I can't find any kind of Selv light that would be suitable for this setup also can't find any info for calcs on voltage drop of a Selv cable.

I suppose I can just use some normal high IP lights as there on the ceiling.

but any advice would be great :)

The voltage drop calculation is the same at any voltage.

Yes FP200 is LSF, but so are a lot of other cable types which are more suitable for the application.
You can get LSF singles, T&E, SWA, flex and flexshield type cable
 
Upvote 0
I probably can get away with not using Selv to me its not doing it properly, but if I did use Selv you mentioned Voltage drop problems could you just expand on that.
 
Upvote 0
Voltage drop is dependent on the length of the cable and the current flowing through it.

So, longer = higher drop... higher current = higher drop.

Lower voltage = higher current for the same power. Work out the current for a 50w 240v lamp and a 50w 12v lamp and that will make it clear.

As for the 'not doing it properly'. There are very specific cases where SELV is mandated, for most other cases an LV supply is totally acceptable and is preferred for the reasons that should become obvious when you run the numbers above.
 
Upvote 0
Voltage drop is dependent on the length of the cable and the current flowing through it.

So, longer = higher drop... higher current = higher drop.

Lower voltage = higher current for the same power. Work out the current for a 50w 240v lamp and a 50w 12v lamp and that will make it clear.

As for the 'not doing it properly'. There are very specific cases where SELV is mandated, for most other cases an LV supply is totally acceptable and is preferred for the reasons that should become obvious when you run the numbers above.

Thanks for your replies, when I say properly I mean adhere to the Regs, it seems I can only just get away with it being in Zone 2 and not needing SELV, one other member also asked about this on the forum, one of the later questions asks you to draw a SELV transformer makes you wonder.......
 
Upvote 0
This is what the regs say about protection for safety and the application of protective measures against electric shock.

"702.410.3.4.3 Zone 2
One or more of the following protective measures shall be employed:
(i) SELV (Section 414), the source for SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source for SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1

(ii) Automatic disconnection of supply (Section 411), using an RCD having the characteristics specified in Regulation 415.1.1 NOTE: Where a PME earthing facility is used as the means of earthing for the electrical installation of a swimming pool or other basin, it is recommended that an earth mat or earth electrode of suitably low resistance, e.g. 20 ohms or less, be installed and connected to the supplementary protective equipotential bonding.

(iii) Electrical separation (Section 413), the source for electrical separation supplying only one item of current using equipment and being installed outside zones 0, 1 and 2. However, it is permitted to install the source in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1."

If you're worried about things like IP rating, you can get away with IPX2 fittings so you don't even need anything special unless it's outside or you're going to jetwash them.
 
Upvote 0
Assuming the Ceiling is Zone 2 we don't even know the height of the room and if there's a diving board it would have to be even higher I.e the ceiling or the walls could be Zone 1 needing SELV.
Looking at the Drawing scale midway up the walls must be Zone 1 breaching the Regs if you put LV lights there.
This is what the regs say about protection for safety and the application of protective measures against electric shock.

"702.410.3.4.3 Zone 2
One or more of the following protective measures shall be employed:
(i) SELV (Section 414), the source for SELV being installed outside zones 0, 1 and 2. However, it is permitted to install the source for SELV in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1

(ii) Automatic disconnection of supply (Section 411), using an RCD having the characteristics specified in Regulation 415.1.1 NOTE: Where a PME earthing facility is used as the means of earthing for the electrical installation of a swimming pool or other basin, it is recommended that an earth mat or earth electrode of suitably low resistance, e.g. 20 ohms or less, be installed and connected to the supplementary protective equipotential bonding.

(iii) Electrical separation (Section 413), the source for electrical separation supplying only one item of current using equipment and being installed outside zones 0, 1 and 2. However, it is permitted to install the source in zone 2 if its supply circuit is protected by an RCD having the characteristics specified in Regulation 415.1.1."

If you're worried about things like IP rating, you can get away with IPX2 fittings so you don't even need anything special unless it's outside or you're going to jetwash them.
 
Upvote 0
The celling of the pool is approx 2.7/2.8m from the floor and therefore is outside of zones. The walls east, north and west are zone 2. The south wall with changing rooms is just outside the zones.
The cables in which you can use have been pre decided for you so too has the the containment method.
The only place I used selv was for the plunge pool as there's physically no other way to get lighting and had the junction box inside the pump Room.
 
  • Like
Reactions: Mark Wright
Upvote 0
The celling of the pool is approx 2.7/2.8m from the floor and therefore is outside of zones. The walls east, north and west are zone 2. The south wall with changing rooms is just outside the zones.
The cables in which you can use have been pre decided for you so too has the the containment method.
The only place I used selv was for the plunge pool as there's physically no other way to get lighting and had the junction box inside the pump Room.
Dude your right it says the ceiling is 2.4m above ffl so only just in Zone 2 Thanks
 
Upvote 0
Sorry, I made a boo boo! The 3 walls are within zone 1 not 2 (thinking of rooms with bath/shower ?), and so the south one is zone 2 just. No given height for plunge pool but as the plans show a level floor and steps leading to plunge then you can guess the celling height is more likely to be less than 2m.
As for fitting lights along the walls as suggested, why? You can use 240v across the celling which will help with that practically impossible 30m max circuit lengths
 
Upvote 0
and I think its
Sorry, I made a boo boo! The 3 walls are within zone 1 not 2 (thinking of rooms with bath/shower ?), and so the south one is zone 2 just. No given height for plunge pool but as the plans show a level floor and steps leading to plunge then you can guess the celling height is more likely to be less than 2m.
As for fitting lights along the walls as suggested, why? You can use 240v across the celling which will help with that practically impossible 30m max circuit lengths
I'm just going with Ceiling lights now but technically Zone 2 is meant to be 2.4m from the floor isn't it? Not exactly happy but......
 
Upvote 0
Haven't got books on me atm and CBA to go to van to get them ?, but I'm pretty sure that anything above 2.5m in height is outside zones. The height of the main pool is over over 2.5m to celling.
The zones go outwards, not upwards.
 
Upvote 0
Zone 2 runs from the floor to a height of 2.5m above finished floor level.
 
Upvote 0
As above you need to remember just because a wall falls within a zone its full vertical height may be outside of it.
 
Upvote 0
Zone 2 runs from the floor to a height of 2.5m above finished floor level.
Just to clarify I'm confused ;) my lights are 2.4m from floor and directly above the pool what Zone am I?
 
Upvote 0
Do you have a current copy of BS7671.
 
  • Like
Reactions: SparkyChick
Upvote 0
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Reading
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Please Help L3 Design Project Selv
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
Mark Wright,
Last reply from
Mark Wright,
Replies
32
Views
5,426

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.