Not sure if this is possible but just putting it out there...
Current Situation
Need to tidy up some of the mess in the garage from the previous owner of the house. Wires going all over the place.
Additionally, all of the upstairs lights, the garage light and an external light are all radial circuits wired into one 6A MCB. This seems not ideal to me as if a fault developed on the outside light with it being exposed to the weather, it would knock out all of the upstairs lighting and the garage light which is where the consumer unit is located.
The consumer unit is split into two "sections" both protected by RCDs.
The right hand side of the unit has (all Doepke):
RCCB (In 63A)
B32 - looks like a ring
B32 - again a ring
B6 - lighting circuit (not the one mentioned above)
B16 - currently a radial to into a un-switched fuse (3A) which runs the house alarm on 2.5mm cable.
B20 - unused
B40 - shower
What I would like to do
For my light installation I was planning on replacing the unused B20 MCB with a B6 and creating a radial circuit, literally 3 metres of 1.5mm cable into the garage into a fused switch which I will then use to feed two external lights. I calculate the max load of the LED GU10s as under 1amp.
However, I am struggling to find a new Doepke B6 MCB at a reasonable price - looks like they are discontinued.
So then I thought can I solve two problems from the existing unused B20 MCB namely:
So could I radial from the unused B20 MCB using 2.5mm cable into a fused switch (13A) for the garage door and another fused switch (1A) for the external lights?
The reason for the switch for the external lights switch being in the garage is because I am planning to use "smart" GU10's which are switched on/off from a server and I just need a way to isolate them in case of fault etc. I don't need to switch them on from inside the house.
If I can do this it would really help me as I would have everything at the right end of the garage and eliminate cable runs etc.
If so, can I loop in/out of a metal clad fused switch, or what would be the preferred way to do this?
Thanks in advance for any help received.
Current Situation
Need to tidy up some of the mess in the garage from the previous owner of the house. Wires going all over the place.
Additionally, all of the upstairs lights, the garage light and an external light are all radial circuits wired into one 6A MCB. This seems not ideal to me as if a fault developed on the outside light with it being exposed to the weather, it would knock out all of the upstairs lighting and the garage light which is where the consumer unit is located.
The consumer unit is split into two "sections" both protected by RCDs.
The right hand side of the unit has (all Doepke):
RCCB (In 63A)
B32 - looks like a ring
B32 - again a ring
B6 - lighting circuit (not the one mentioned above)
B16 - currently a radial to into a un-switched fuse (3A) which runs the house alarm on 2.5mm cable.
B20 - unused
B40 - shower
What I would like to do
For my light installation I was planning on replacing the unused B20 MCB with a B6 and creating a radial circuit, literally 3 metres of 1.5mm cable into the garage into a fused switch which I will then use to feed two external lights. I calculate the max load of the LED GU10s as under 1amp.
However, I am struggling to find a new Doepke B6 MCB at a reasonable price - looks like they are discontinued.
So then I thought can I solve two problems from the existing unused B20 MCB namely:
- The external lights
- The roller shutter garage door which is currently connected to a plug socket at the other end of the garage and causing a cable run I would like to remove.
So could I radial from the unused B20 MCB using 2.5mm cable into a fused switch (13A) for the garage door and another fused switch (1A) for the external lights?
The reason for the switch for the external lights switch being in the garage is because I am planning to use "smart" GU10's which are switched on/off from a server and I just need a way to isolate them in case of fault etc. I don't need to switch them on from inside the house.
If I can do this it would really help me as I would have everything at the right end of the garage and eliminate cable runs etc.
If so, can I loop in/out of a metal clad fused switch, or what would be the preferred way to do this?
Thanks in advance for any help received.