farmerian

Is there a maximum r1 rn and r2 value for a ring main ?
I no the maximum ZS is 1.10ohms for a 32amp type B curve breaker but is there anything in regs for the end to end resistance of the ring ?
 
Maybe I got the max zs value wrong for that protective device,, but what I am asking is they anything in regs for end to end values for a ring circuit ?
 
Is there a maximum r1 rn and r2 value for a ring main ?
I no the maximum ZS is 1.10ohms for a 32amp type B curve breaker but is there anything in regs for the end to end resistance of the ring ?

Haven't got Yellow OSG with me at the moment, but Table 7.1 (i) of the Green OSG gives some maximum cable lengths for ring circuits with varying protective devices, so in effect giving max r1, rn & r2. I guess the Yellow version values with differ from the Green book due to the new 0.95 factor!
 
Well, I'd say your Zs, so comply would have to be say 1.1 or less, so I suppose the worst case scenario for R1+R2 would have to be no more than 1.1 - 0.35 which would be the lowest out of the supply types.

i suppose this is hypothetical and calculated opposed to measured anyway. So suppose you did that you R1+R2 would have to be no more than 0.75,

im probably totally wrong but I suppose if you were to calculate it on paper for a TNCS supply type I'd say your max figures would be the following based on 2.5/1.5

R1+R2 = 0.75
r1 = 0.56
rn = 0.56
r2 = 0.94

its only a stab in the dark and probably wrong.
 
Recommended max floor area for a RFC is 100m2 iirc. There is no maximum figure for r1,r2 etc as such, as ultimately, it's achieving less than the max Zs which will be the determining factor.
 
Recommended max floor area for a RFC is 100m2 iirc.

That was simply a historical requirement. The 17th Edition removed it so there is no 100m^2 maximum anymore.

As said if the circuit is designed for 0.4 second disconnection and non-excessive voltage drop then that is the limit.
 
Just to add to my post, I think off the top of my head 2.5 has a resistance of 7.41 mopm I think...

so so take my calculated R1+R2 of 0.75 ohms x 1000, divide by 7.41 that gives you 75m
 
and probably wrong.

You're out by a factor of two. The maximum value of r1+r2 cannot be more than 4 times the maximum R1+R2, because the highest resistance will occur halfway round the ring where it is served by two legs of half the total length in parallel, each of (r1+r2)/2.
 
You're out by a factor of two. The maximum value of r1+r2 cannot be more than 4 times the maximum R1+R2, because the highest resistance will occur halfway round the ring where it is served by two legs of half the total length in parallel, each of (r1+r2)/2.

Oh yes, why did i divide it by 4? No idea, I know it's two. Thanks for the correction.

i was on the right lines but out if that makes sense.
 

Reply to Ring Main resistances in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
661
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock