The more you mull it over, the less unconventional it will seem. Believe me, by nature I, m very cautious and "doing things once and doing it right" is my natural way. In the electrical Industry we are taught to follow the regs rigidly. Correct. However, breaking with convention in order to improve matters is in my experience not really encouraged. It tends to be a case of "that's, how we have always done things". However, it's clear that someone somewhere is doing this, otherwise we would never have new regs and new improvements. I never challenge convention for the sake of it. There must be a very definate practical goal.I was going to edit that post, but figured you get that I was referring to the use of boards with significant capacity and not 3 phase installations.
[automerge]1596579736[/automerge]
I'm very much in favour of breaking with convention, when doing so fulfills a need or improves upon convention - whether that be a one off circumstance or in a more widespread manner.
What I struggle with here are the potential limitations placed upon homeowners as that house could have new occupants 2 or 3 years from now, with very different requirements to the current occupant. It may be that you have got this installation bang on the money for the style of property, but I can only consider the issue from my own perspective and limited experiences. Your ideas may not meet with universal approval, but I like that they challenge convention and give me something to think about.
Just a point.
Two rings or not, in general, what are FIRST thoughts on four (or more) cables in a circuit breaker terminal, whilst carrying out an EICR?
How long is a piece of string, maybe?
Is that any worse than a multi stranded 6mm or 10mm cable?
Always seems strange to me sparks dont bootlace these.
Yes it is different to a coarse stranded cable. Coarse stranded cables have the strands compacted tigether at manufacture and they are further compacted together by the termination. Multiple seperate conductors terminated together can, if not done properly, result in one conductor not being clamped at all.
Ferrules are only required for fine stranded cables as screw terminals can cut through the strands or spread them out so that good contact is not made.
Coarse stranded conductors don't suffer from these same issues if correctly terminated.
Just looks strange to me where I’d almost always see some sort of crimp even on corse stranded cables.
When/where would you always see some sort of crimp on coarse stranded?
Offshore oil and gas/petrochemical is where I work mainly.
Seems to be fairly standard practiceon the sites I’ve worked on.
OK, so that's a specialised industry with its own rules and regulations, not really something you can compare to general installation work.
What type of crimps are used on coarse stranded cables? Are you talking about ferrules or something else?
Will also be seen on all BMS panels
Not sure, at the time (approx 11-9 years ago) we were undertaking work for around 3 BMS firms, and all their panels had it, even the panels internal 13amp socket outlet.It just seems weird to me that bootlace ferrules are being used on coarse stranded cables.
[automerge]1597007912[/automerge]
Any idea why?
Bootlace Ferrules on say 6 mm conductors seams to be the new YouTube electricians fad, one does it they all do it, spacing rcbo’s when the circuits are likely to be lightly loaded is another, monkey see monkey do.It just seems weird to me that bootlace ferrules are being used on coarse stranded cables.
[automerge]1597007912[/automerge]
Any idea why?
Yeah true but like I say , I mostly see this at CB terminalsIf the circuit breaker has a cage connector I agree, but not when putting a multi strand cable into a standard screw connector, can't guarantee the whole of the cable is connected securely the strands that are not under the screw are a potential ark point.
Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??
If so does this meet the current regs.
TIA.
May I be the devil's advocate?
2 small ring final circuits could be connected in series to provide one rfc and thus could be connected to one OCPD. Quote Reply Report Edit
Source URL: Ring main. - https://www.electriciansforums.net/threads/ring-main.185730/
Trying to get my head around how you wire 2 RFCs in series.
Aye, 3 through crimps and you're away, no probs......and if Zs a touch high you could leave the cpc's as they are.May I be the devil's advocate?
2 small ring final circuits could be connected in series to provide one rfc and thus could be connected to one OCPD. Quote Reply Report Edit
Source URL: Ring main. - https://www.electriciansforums.net/threads/ring-main.185730/
Think we know what ackbar means though, don't we?Trying to get my head around how you wire 2 RFCs in series.
Aye, 3 through crimps and you're away, no probs......and if Zs a touch high you could leave the cpc's as they are.
[automerge]1597960211[/automerge]
Think we know what ackbar means though, don't we?
In all honesty I cannot see anything in Bs7671 that this would contravene other than good workmanship. If it originates from one MCB it is a single circuit. Despite what has been said about it overloading there is no reason to assume it would be. A single ring with 10 double sockets could have 20 3kw heaters plugged into it.
Very poor practice though and it needs altering on that basis.
edit. Post crossed with Sparkychick who has reached the same conclusion.
You're right, 2 RFCs in 1 OCPD = 1 circuitSurely two ring finals connected in series would no longer constitute two circuits and, as such, would only be once circuit connected to the MCB?
To be clear; I'm asking a question, rather than telling you that you're wrong
Absolutely no chance should there be 2 RFC in a 32A MCB. Neither should there be a 2.5mm2 radial let alone 2,3 or 4. It is covered in the regs and is further legislated against in test and inspection.
Firstly assuming it is 2 RFC then it is in-fact an interconnected ring main which is the whole purpose of the ring final test to avoid. The reason for avoiding is simple should either of the two rings of an interconnection become open circuit then the circuit becomes two or even four radials.
Which also answers all other scenarios the 2.5mm2 Cables of a radial circuit on 32amp supply will become over loaded and be a potential fire hazard.
Also it becomes problematic when conducting test or fault finding.
Absolutely no chance should there be 2 RFC in a 32A MCB. Neither should there be a 2.5mm2 radial let alone 2,3 or 4. It is covered in the regs and is further legislated against in test and inspection.