HI,Can anyone answer a query i have.if i run a cable in a brick porch,on the house wall and within 150mm from the corner is this classed as a safe zone .the cable is rcd protected,would i need to run in conduit.the wall has decrotive pannelling,thanks
 
when you say in a brick porch, do you mean on the surface, or behind panelling?
 
Last edited:
Yes as per reg 522.6.6 (v) a cable can be installed within 150mm from the top of the wall or partion or within 150mm of an angle formed by adjoining walls or partion.

As the cable is RCD protected then no need to run in conduit unless the cables are singles and then they would have to go into some form of containment. Though if your burying T+E cable IMO it's best to offer the cable some form of mechanical protection and oval tube is normally used., but that's just my preference you can bury direct if you wish.
 
It would be behind wooden pannelling.but i thought if i run it within 150mm of the corner(created by the walls of the porch)that would be classed as safe zone
 
correct. safe zone, no problem
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Safe zones
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
safe zones

Advert

Thread statistics

Created
waynelester,
Last reply from
telectrix,
Replies
4
Views
1,808

Advert