Search the forum,

Discuss shop storage heater in the UK Electrical Forum area at ElectriciansForums.net

multimick

-
Esteemed
Arms
Reaction score
289
small shop has one 2.5kw storage heater on one off peakcircuit via fcu however the shop only opens five days a week so are asking for a timer (7 day) so they can save heating an empty shop when not open.If i put a timer on off peak circuit it will stop at 8 in morning . Any ideas?
 
Install a 7 day timer, and match the timings or full 24hours during 5 day opening, and switch off at weekends.

Just to add, the timer will need to be run off normal cu to keep it running, and would suggest a contactor to control the storage heater
 
Last edited:
Use a 7 day timer with contacts which are separate from the timer supply. Run the timer off the continuous supply (suitably fused). Route the heater supply through the timer contacts.
 
Used the standard cu to power the timer and contactor......then contactor controls heater..

Din Contactor.jpg
 
Last edited:

Reply to shop storage heater in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.