Jan 27, 2023
York
Electrical Enthusiast (Unqualified Hobbyist etc)
I've mocked up a small garage circuit, does this look fine, any issues? thanks
It looks all wrong to me anyhow 😁
10 metre swa run, no extraneous. cheers
  • Funny
Reactions: DPG
personally I would go bigger than 2.5 to the garage from the inside DB, you will use all sorts of power eventually, 2.5 is too small really, and go bigger than a 20 amp MCB via the RCD as well, JMO.
I would put the feed on its own supply, as a fault in the garage will take half the house out
Ideal world though. It's reasonable to feed from one half of the CU for a modest garage install.
cheers for the input guys
Reactions: DPG
Better to adapt/convert the house CU so that the garage is fed from an MCB that is not RCD-protected.
(aka a "high-integrity" CU - who invented that ridiculous title?)
Locate the RCD at the garage end to replace the isolation switch. Then, if there is an earth fault, that will only trip the garage RCD and not half the house.
The SWA does not need RCD-protection, as it runs all the way from the house CU to the garage.
Depends if ADS is satisfied without an RCD.
  • Agree
Reactions: mainline
York
Small garage circuit
mavezy,
westward10,