I take it that's under the consumer unit? If so I very much doubt it will reach to redo this with a correct gland & banjo without either renewing it or a join or isolator of some kind.

It is. There is some excess cable under the kitchen units in the next room.
 
  • Like
Reactions: Chivers
I take it that's under the consumer unit? If so I very much doubt it will reach unless there's an amount of slack to redo this with a correct gland & banjo without either renewing it or a join or isolator of some kind.
I wouldn't be glanding with banjos (or earthing nut) in that plastic CU, anyway. It requires a metal adaptable box fitting below the unit. Swa glands in plastic.....horrible!
 
  • Like
Reactions: brucelee
I wouldn't be glanding with banjos (or earthing nut) in that plastic CU, anyway. It requires a metal adaptable box fitting below the unit. Swa glands in plastic.....horrible!

"REQUIRES" is a strong word.
I would prefer to make off into a metal enclosure but if the cable is supported correctly, a plastic enclosure can be glanded off correctly with either a banjo or earthing nut.
 
I wouldn't be glanding with banjos (or earthing nut) in that plastic CU, anyway. It requires a metal adaptable box fitting below the unit. Swa glands in plastic.....horrible!

A steel through box is another good option, it has an earth terminal in it already to make the connection to the armour nice and easy.
 
  • Like
Reactions: brucelee
"REQUIRES" is a strong word.
I would prefer to make off into a metal enclosure but if the cable is supported correctly, a plastic enclosure can be glanded off correctly with either a banjo or earthing nut.
Depends how you take it...in my view it does require it, taking into account those flimsy plastic units.
 
  • Agree
Reactions: Robson689
A well supported swa cable, adds no strain to the enclosure. In some ways it makes it more rigid.
 
in the OP's case, the installer has cut big holes in bottom of CU, so a through box is required here. 1. to gland the SWA, and 2. to restore the IP rating of the CU.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA questions, doubting electrician
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
LeeH38,
Last reply from
telectrix,
Replies
46
Views
7,485

Advert