I wonder if I might throw an SPD-shaped spanner in the works here?

If the guidance in the On-Site Guide (section 3.6.4, page 41 of the little brown book) is that dual RCD metal boards are not suitable on TT systems due to the risk of the single-insulated L feeds to the RCCBs making contact with the metal box, presumably the same argument could be made for situations where the L feed to an SPD inside the metal DB is in the form of a single-insulated cable? In which case a time-delayed RCCB acting as a main switch might be a good idea. 534.4.6 (concerning fault protection of SPDs), and figures 16A2 and 16A3 of Appendix 16 refer. Of course, your SPD will not protect your upstream RCCB in this case.

If your SPD is fed directly from the bus bar - such as the single module Wylex SPDs - then this is equivalent to having all RCBOs, a situation that the OSG says an upfront RCD would not be required (though of course it may be needed, or desired, for other reasons).
 
... and reading a bit further on in the big brown book, 534.4.7, SPD installation in conjunction with RCDs:

Where SPDs are installed in accordance with Regulation 534.4.1 and are on the load side of an RCD, and RCD having an immunity to surge current of at least 3kA 8/20 shall be used.
NOTE 1: Type S RCDs in accordance with BS EN 61008-1 and BS EN 61009-1 satisfy this requirement.
Installation of Type 1 SPDs downstream of an RCD is not recommended.
NOTE 2: In the case of a surge current higher than 3kA 8/20, the RCD may trip causing interruption of the supply.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Stafford
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
T T consumer unit upgrade
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Ade1309,
Last reply from
happysteve,
Replies
23
Views
4,388

Advert