A time delayed rcd is not required.Hi I am installing my first tt system consumer unit I understand that I need a 100 amp time delayed rcd main switch but can I use rcbos in line next to them or Mcbs and does any one know of a lockable board as I need to install it vertically thx
A time delayed rcd is not required.
Because a time delayed RCD is not a requirement as long as certain conditions are met.Why not? We have no information about what protection is required for any of the circuits so how can you make that decision?
Hi Mainline.Because a time delayed RCD is not a requirement as long as certain conditions are met.
This should explain it better than i can.Hi Mainline.
Could you outline those conditions for the original poster please?
Because a time delayed RCD is not a requirement as long as certain conditions are met.
A TIME DELAYED rcd is not required, the op said he was using rcbos.But you stated categorically that it is not required with no mention of any conditions to this.
A TIME DELAYED rcd is not required, the op said he was using rcbos.
Required means: compulsory, or otherwise considered essential; indispensable.
I think you are missing the point.The OP asked if he can use RCBO's
Again, how do you know it is not required with no details of the installation? We have no details of the installation at all, other than it has a TT supply and may have RCBO's, MCB's or a mixture of both.
Without further detail I fail to see how you can state that a time delayed RCD is not required.
Even if this is a simple domestic installation there may be circumstances where a time delayed RCD is required.
Although SP rcbos comply, I do agree that DP rcbos are the way to go whether TN or TT not just from the safety aspect but also the fault and testing side of it.I thought TT systems needed to have DP isolation if tripped (would have to look that up though) and not all RCBOs offer that?
So for some cases you might not need the up-front delay RCD, but it is not a simple 'no' due to that aspect. Also being a bit paranoid I would rather not have a failed/sticky RCBO allowing the whole installation CPC (and any connected external metalwork) to be elevated to near full mains voltage, with an up-front delay RCD you at least avoid uch a single point of failure.
N-E fault would trip the RCD if RCBOs didn't break both poles. this would contravene the one out, all out reg.Isolation on TT should isolate all poles, circuit protection only needs to disconnect the line conductor/s.
I think you are missing the point.
It doesn't make any difference not knowing about the installation, it doesn't change the fact that:
The use of a timed delayed RCD is NOT a requirement.
Maybe I amissing your point, please do explain what your point is??
Are you saying that every consumer unit that's fitted with SP rcbos aren't compliant ?N-E fault would trip the RCD if RCBOs didn't break both poles. this would contravene the one out, all out reg.