One post seems to contradict the other here, you can't start the system but then it trips overnight


If a brand new RCD is tripping at that level I would be speaking to the manufacturer about a replacement, out of the box problems with RCD's seem to be getting more common in the last few years
The initial tripping was intermittent and would happen overnight. The system would operate happily for 3-4 days then trip out.
This led me to believe that a fault had developed on one or more of the heating components as the customer was turning off the 2 top floor heating system and no tripping would occur.

It was only when I was on site and tripping happened that I made the discovery that the tripping would happen when the UFH called for the boiler to fire and the pumps started up.
On Friday the system would always trip with all the UFH systems on so the 2 top floor UFH systems were switched off.
After my initial discussions on here I asked the customer 2 switch off the ovens and the hob, at the wall, on that side of the CU. They then turned on the 2 top floor UFH systems and no tripping occurred.
It was left like this from 11:00 until 16:00, then they switched the ovens and hob back on with no tripping.
Until they got up this morning and the RCD had tripped.
I'm now heading down the path of cumulative leakage current. More testing required.
 
19ma is low for a Hager RCD imo. I'd try moving it on another RCD.

It seems unlikely as I've fitted hundreds with extremely few problems, but maybe the RCD is faulty.
 
No leakage clamp meter as yet, any recommendations?

No leakage clamp meter as yet, any recommendations?
There is no N link between the boiler and the UFH as the wiring centres use a 0v built in relay to send the demand signal.
The remote Grundfos pumps and 2 port valves are controlled by the boiler spur, so I could separate the UFH and the boiler to 2 RCBOs
Good ones aren't cheap, sadly. I had a Metrel one (can't remember the model) that was amazing as it would even give you an indication of the nature of the current, lead/lag, pf etc etc which was genuinely helpful in understanding what was going on in the circuit, cost about £400ish ten years and some pikey stole it in a van break-in. Now you can get good ones for half that.
 
Good ones aren't cheap, sadly. I had a Metrel one (can't remember the model) that was amazing as it would even give you an indication of the nature of the current, lead/lag, pf etc etc which was genuinely helpful in understanding what was going on in the circuit, cost about £400ish ten years and some pikey stole it in a van break-in. Now you can get good ones for half that.
Thanks for that, I've been reading reviews and ordered the Megger DCM305E £220.
Hopefully it will help to get to the bottom of my problem.
 
It's always good when we can prove beyond doubt the cause of a fault with our nice expensive test gear, but once in a while you'll be up against a truly intermittent fault that only shows very occasionally and for a split second.
In these cases you have to set up experiments, such as moving to a different RCD, and then wait for the fault to gradually give itself away .
 

Reply to Wet UFH pumps causing RCD tripping in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
890
A combi is heating 5 ufh zones downstairs and 1 radiator zone upstairs. It has a two port valve for each. My question is, would you fit this with...
Replies
4
Views
1K
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
753
Hi. I’ve recently had installed a manifold (including zone valve and pump) for the newly installed Wet UFH in my extension. The system is split...
Replies
14
Views
3K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock