Trainee Electrician
Hi Guys, how would you wire three gang two way switch for emergency lights so you have 3 feeds coming to the switch aswell as 3, 3 core and earth going to the light aswell as 3, 3 core and earth being strappers to the others 3 gang two way switch new to electrics so help would be appreciated cheers
 
Lets get this straight... you have 3 rows of lights(?) all 2 wayed from 2 positions. 3 switches at each door or whatever.
You are adding an emergency light?
You need an unswitched live in addition to any switchwire or neutrals to the emergency fitting. Looping through other fittings if nessecery.
You may want to switch this live through a keyswitch... which would mean one of your 3 gangs need to be 4 gang

You could draw out a circuit that you think it needs, and we will see if you’re on the right track
 
The way it was wired there was 9 cables at the switch 6, 3 core and earths and 3 feeds would it be the 3 brown feeds to the com neutrals in wago and earths in wago plastic fitting. Use the 3 greys going to the light as switch lines and put the blacks in wagos as neutrals. And for the strappers 3 core and earths put the brown in the com. and black in wago and grey in wago. The electrician who wired never told me how he wired it just asking would you know what he did
 
Don’t use black as N . Sleeve the grey with blue

Use black sleeved brown as a swi line

Although some will disagree and use black sleeved brown as perm live and brown as swi line
 
  • Agree
Reactions: Zdb
So if I use brown as permanent black as switched live and grey as neutral is that the correct way to wire the three gang two ways switch
 
Providing all cores are correctly identified it is irrelevant whether you use black or grey as neutral. There is no set rule to this.
 
For the strappers is it ok to put the black and grey in wagos as long as the brown goes the the com of the two switches
 
What do you do with black and grey for strappers
 
What do you do with black and grey for strappers

Brown sleeving in both to distinguish them as live conductors (switch wires)

You’re not really changing what the previous spark did, so how he wired it is irrelevant.
You are adding one core, supplying an emergency fitting with a permanent live which isn’t there at the moment.
 
No it wasn't, there has never been a 'de neutralising'

I had a thing from the niceic around the time of harmonisation it was a big A4 leaflet about de neutralise black when converting old colours to new. Think several cable manufacturers also produced their own leaflets of de neutral black as well...

It’s even in the brown on site guide I think

Will try to dig it out later
 
I had a thing from the niceic around the time of harmonisation.

It’s was a big A4 leaflet about de neutralise black when converting old colours to new.

It’s even in the brown on site guide I think

Will try to dig it out later

All I have ever seen is advice about old colours and how they correspond to new colours, but not how to oversleeve harmonised colours for different uses.
 
Not a Regulation then.
 
All I have ever seen is advice about old colours and how they correspond to new colours, but not how to oversleeve harmonised colours for different uses.

The official guidance from the iee and niceic at the time was to not use black as neutral post harmonisation.
It was to use grey sleeved blue.
Black sleeved g/y
 
The official guidance from the iee and niceic at the time was to not use black as neutral post harmonisation.
It was to use grey sleeved blue.
Black sleeved g/y
Like I say, I have never seen that guidance written anywhere, heard it plenty of times though and it is the convention I tend to use.
 
I had a thing from the niceic around the time of harmonisation it was a big A4 leaflet about de neutralise black when converting old colours to new. Think several cable manufacturers also produced their own leaflets of de neutral black as well...

It’s even in the brown on site guide I think

Will try to dig it out later

The niceic made up that nonsense but as far as I know it never featured in the regulations.
[automerge]1569226857[/automerge]
The official guidance from the iee and niceic at the time was to not use black as neutral post harmonisation.
It was to use grey sleeved blue.
Black sleeved g/y

Do you have any evidence of the iee supporting this?

The convention was to use red for live, yellow for another live or earth and blue for neutral. Red became brown, yellow became black and blue became grey, so to continue the same convention Black is used for live or earth and grey for neutral.
This can keep joints between the two neater/easier as the cores should naturally line up if you have the cable the right way round.
 
The niceic made up that nonsense but as far as I know it never featured in the regulations.
[automerge]1569226857[/automerge]


Do you have any evidence of the iee supporting this?

The convention was to use red for live, yellow for another live or earth and blue for neutral. Red became brown, yellow became black and blue became grey, so to continue the same convention Black is used for live or earth and grey for neutral.
This can keep joints between the two neater/easier as the cores should naturally line up if you have the cable the right way round.

Yes black becomes a live or earth

The grey became the neutral

If adding new cable to an old installation

That was the official recommendation iirc
[automerge]1569227593[/automerge]
Will try to dig out my old brown on site guide later and take a picture
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Wiring emergency lights
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Scifen,
Last reply from
Dustydazzler,
Replies
19
Views
4,366

Advert