Hi, recently I have found that my Fluke 1653 has been tripping the odd RCD when doing a three lead Zs(loop) test. I can't understand why, it has not done this before.
 
if your tester puts 15mA through for the test and there's inherent leakage of 8 -10 mA on the installation, it may well trip. do a ramp test first .
 
  • Like
Reactions: 1 person
  • Like
Reactions: 1 person
I've had this before, it was a 100mA main switch RCD, on 2 of the circuits cooker and ringmain, the RCD would trip on loop test l, turns out a screw was put through the cooker cable with a dead short on N-E, or try a Ramp test, and I take it your on No Trip mode, goodluck
 
Look on the plus side as well , now you've done the test with all circuits connected as well and found RCD trips , you now know theres a fault on one of the circuits or appliances , but as already said RCD tests are best done at the board as appliances such as fridges etc will give false readings anyway..

oops just re read the ops question , Zs testing not RCD ..still same applies ,
 
Last edited by a moderator:
plug the blue lead in aswell :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs test tripping RCD.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
markadams,
Last reply from
TJ Anderson,
Replies
10
Views
7,518

Advert