Beeg
97
22
83
UK
Hi all,
Just a quick question. Would a new installation for an outside light require an RCD switch if there is no RCD protection at the CU? The cable will be clipped direct to inside of porch wall.
Beeg
it would be fine. however if done this year, not necessary.
After the new year, the RCD protection will have to be at the Consumer Unit.
In domestic installations, anyway.
So if done before end of year a conventional 1G 1 way switch would conform to regs and no RCD protection would be necessary?
Yes, unless the cable is concealed in a wall at a depth less than 50mm and requires RCD protection.
I must have missed this, not that I do domestic.
What reg mate?
Does that go for anything being added to a circuit?
411.3.4 Additional requirements for circuits with luminaires
Within domestic (household) premises, additional protection by an RCD with a rated residual operating current not exceeding 30 mA shall be provided for AC final circuits supplying luminaires.
It will be the same for lighting circuits, as it is for circuits of locations containing baths or showers.
Any additions to existing circuits will require the whole circuit be protected.
The light itself does not require RCD protection.
Depends on the siting of the luminaire. At high level on a wall connected to the building then it won't, but otherwise it may well.
Sorry for the confusion mate.
I knew about lighting circuits needed RCD protection but your comment about "the RCD protection will have to be at the Consumer Unit" that I don't know about.
It sounded like, if you are adding an outside light, what the OP is suggesting using will not be to regs.
The new requirement is for circuits supplying luminaires to be RCD protected, just the same as it is now for circuits of locations containing baths or showers and socket circuits in horticultural/agricultural installations.
Any addition to an existing lighting circuit, will require RCD protection be provided for the existing part of the circuit, not just the addition.
So yes the RCD protecting the circuit will have to be at the CU.
Reactions: suffolkspark
Im not disagreeing with this, but surely the easiest way is to protect your additional light fitting via a RCD FCU the circuit would start at the point of of the FCU.
Looking up the definition of circuit
CIRCUIT. An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)
Not trying to be a pain mate but I thought, maybe wrongly, that if adding a light to a circuit it was just the additional circuit that needed RCD protection and not the whole circuit from the CU.
Just to clarify, if I was to have it installed before the 18th edition is enforced next year, what would a sparkie need to do in terms of RCD/ switched FCU etc for it to meet current regs?
The fitting will be connected to the downstairs lighting circuit from an existing ceiling rose.
Cable will be clipped to wall around inside of porch and then pass through wall to light fitting at a depth greater than 50mm
Not done any researhe yet on te 18h, Why in thu=is scenario would yt be nessessar at the CU, Not done any auto correct cos it is Satruday night,
Recently we had this thread: Does this setup contravene any regs or is it ok? - https://www.electriciansforums.co.uk/threads/does-this-setup-contravene-any-regs-or-is-it-ok.167990/
It really thought that we had established that the origin of a final circuit is at the DB/CU?
Now if people want to consider an FCU to be the origin of a final circuit, then fine, do so.
Just remember Regulation 314.4:
“Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated.”
For those of you who want to drag up the definition of a DB/CU, and say that an FCU is a DB/CU.
Just remember Regulation 421.1.201:
“Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12.”
Yes, with additions and alterations, only the new work has to comply with the current Regulations.
That’s fine if you are adding a socket to an existing socket circuit with no RCD protection, only the new socket and perhaps the new cabling will require RCD protection.
However, where the requirement is for a circuit to be provided with RCD protection, then in order to comply, the circuit will require RCD protection.
The scenario you describe will not require RCD protection.
In fact, if you design the alteration now, then you can install after the 18th has come into force and still not require RCD protection.
Reactions: AJshep
Beeg
UK
Outside light RCD protection
Lighting Forum
Beeg,
Beeg,