S
Siholtye
Question 48 on this mock paper I have asks,
A 3-Core, 2 Metre flex, has a calculated earth bond reading of 0.152 Ohms. Which nominal conductor c.s.a would this relate to:
A 0.75mm²
B 1.00mm²
C 1.25mm²
D 1.5mm²
What is the answer, how do you calculate it, and where in the COP is this info please?
I'm going to dive straight in... welcome to the forums :)
How do you think you would calculate it?
Welcome to the forum.
The question appears to mix up two different disciplines: fixed wire testing and in service inspection and testing.
I am assuming the question is about in service inspection and testing since you mention the COP.
Appendix VI contains the resistances of flexible cords, which would be your reference for the answer.
However the answer does not match with the method of testing the "earth bond" as the measurement should only encompass the circuit protective conductor of the flex, yet the question appears to be assuming an R1+R2 value for the calculated "earth bond".
The CoP has this Table for cable resistance in the Appendices but unless I am misreading their question is incorrect.20190106_122755.jpg
I was wondering whether the figure they provided was actually an R1+R2 value because 0.152/4 (2m there and back) = 0.038... 0.001 ohms off the figure for 1m of single 0.5mm
Reactions: JDTH
PAtesting generally only refers to the cpc reading as it is the only prescribed continuity test.
Reactions: SparkyChick
Wierdly worded question but I doesn't the 0.152 value given include 0.1 Ohms for the appliance?
(not that they mentioned any appliance)
2 Metres at 0.75 mm2 gives a resistance value of 0.052 Ohms
I do believe you have solved the problem we have overlooked the 0.10 ohm to be added to the cable resistance.
I think patdev has it.
It would have been just so easy for the question to state "calculated maximum permissible earth bond reading of 0.152Ω"
A calculated reading is what reading you would expect to see on the meter when you test and not the maximum reading you could get to allow the tested equipment to pass.
I am obviously still learning the language of C&G speak !:(
Exam question
Electrical Testing & PAT Testing Forum
Siholtye,
Richard Burns,