If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Hi - Just joined the forum as I'm making a career change and am training up.

I've come across some mock papers online and am concerned that either I'm way off or they're wrong, so would love some input. (Exams here)

Given that the resistance per metre of 2.5mm² cable is 7.41mΩ/m at 20°C , what would the approximate R1+R2 reading be at the at the extreme end of a 25m long 20A radial socket outlet circuit?

Possibile answers are

  • 0.27
  • 0.37
  • .074
  • 0.17

I came out with 0.37 using BS7671 and GN3 but the exam confirmed .17 as the answer. Could anyone take a look and tell me what I'm missing/where to find the missing info in either book? Thanks!
 
I concur with you. It is a badly written question but we must assume the cpc is also 2.5, it normally states this. Not sure where they got 0.17.
 
Upvote 0
You would get 0.37 if the line and CPC were both 2.5mm

Are they referring to 2.5mm T&E where CPC is smaller?

Edit, beaten to it by Westie!
And also corrected my own mistake!
 
Last edited:
Upvote 0
I concur with you. It is a badly written question but we must assume the cpc is also 2.5, it normally states this. Not sure where they got 0.17.
Thanks for taking the time! It's really disconcerting when I'm trying to revise and the certainties are wrong!

The following question tried to state that polarity is to ensure that "The resistance is low enough to operate the protective device within the specified time"... Not sure how much I should trust this place.
 
  • Like
Reactions: DPG
Upvote 0
Thanks for taking the time! It's really disconcerting when I'm trying to revise and the certainties are wrong!

The following question tried to state that polarity is to ensure that "The resistance is low enough to operate the protective device within the specified time"... Not sure how much I should trust this place.

It's amazing how many bad questions there are out there. Lots badly worded or vague, but some that are just plain wrong unfortunately.
 
  • Agree
Reactions: Jevans1996
Upvote 0
It's amazing how many bad questions there are out there. Lots badly worded or vague, but some that are just plain wrong unfortunately.
Good to know it's not just me. I'll almost certainly be back with more haha. Cheers!!
 
Upvote 0
Have you paid money for this?
 
Upvote 0
Have you paid money for this?
It was a one time £19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I could find, so it's quite frustrating
 
  • Like
Reactions: westward10 and DPG
Upvote 0

Similar threads

R
Replies
15
Views
5K
R
D
Replies
16
Views
6K
A

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
West Midlands
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Question help needed - C&G 2391 - 52
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Jevans1996,
Last reply from
Jevans1996,
Replies
7
Views
1,757

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.