Hi all, I'm after a second opinion before I allow somebody to do the work on my garden in Yorkshire.
I got a few quotes from qualified electricians to run electrics from the house to a garden room (approximately 6m away). Each electrician (including the one I instructed) made mention of the need for an armoured cable for the run from the house to the garden room. It will be buried under the lawn.
However, when the electrician started the work we noticed that he was not using armoured cable. We queried this and he said that it isn't necessary, providing the right cable size is used, has an isolation fused spur inside the house and is protected by the RCD of the consumer unit. Is this correct?
 
The cable must be suitable for the purpose to which it is put. Do you know what type of cable it is, and how it is being protected? A picture would help...
 
What kind of cable has he supplied , this may have an influence between the quotes and given him an advantage.
I agree with @Cid , he should supply what he has quoted for or better.
 
  • Agree
Reactions: Pete999
If he quoted for an armoured cable then that is what should be used!

However armoured cable is not necessary provided it's adequately protected, ie in conduit

I'd use swa cable as well, but I would also install in some twin walled ducting, as its being buried under ground.
 
I'd use swa cable as well, but I would also install in some twin walled ducting, as its being buried under ground.
What is twin walled ducting?
 
Thanks all, I check on the cable when I get home tonight. He was planning on burying it in some flexi hose, so that wouldn't protect it in any way. My concern was about somebody putting a spade through it or something in the future.
I'll check and get back to you :)
[automerge]1575392018[/automerge]
Thanks all, I check on the cable when I get home tonight. He was planning on burying it in some plastic flexi hose, so that wouldn't protect it in any way. My concern was about somebody putting a spade through it or something in the future.
I'll check and get back to you :)
 
However, when the electrician started the work we noticed that he was not using armoured cable. We queried this and he said that it isn't necessary, providing the right cable size is used, has an isolation fused spur inside the house and is protected by the RCD of the consumer unit. Is this correct?

Cable size, type of isolator and RCD protection have nothing to do with what can, or cannot be buried underground.

Any directly buried cable must be approved by the manufacturer for such use and the regulations require that the cable have an earthed metallic screen or armour (which must be capable of handling the maximum fault current)
Alternatively the regulations allow underground cables to be in a suitable duct (the duct must comply with the British standards mentioned in tbe regulations) and the cable would need to be approved for this use by the manufacturer.

Steel Wire Armoured (SWA) cable satisfies the requirements for direct burial and is the most commonly used cable for this purpose.
There are other types of cable which comply but you won't normally find them used on a domestic installation or commonly available.
 
Steel Wire Armoured (SWA) cable satisfies the requirements for direct burial and is the most commonly used cable for this purpose.
There are other types of cable which comply but you won't normally find them used on a domestic installation or commonly available.

I know your picky about being picky, but some cable manufacturers don’t recommend installing their swa cables direct in ground with high water content, e.g. under a lawn. Hence the recommendation to use ducting. :)
 
I know your picky about being picky, but some cable manufacturers don’t recommend installing their swa cables direct in ground with high water content, e.g. under a lawn. Hence the recommendation to use ducting. :)

I've never come across that before, do you have any examples?
SWA is not suitable for long term immersion in water and most state this, but I've not yet seen reference made to wet ground or lawns.

It does make some sense, but it's hard to know how wet is too wet.
 
Hi all, I'm after a second opinion before I allow somebody to do the work on my garden in Yorkshire.
I got a few quotes from qualified electricians to run electrics from the house to a garden room (approximately 6m away). Each electrician (including the one I instructed) made mention of the need for an armoured cable for the run from the house to the garden room. It will be buried under the lawn.
However, when the electrician started the work we noticed that he was not using armoured cable. We queried this and he said that it isn't necessary, providing the right cable size is used, has an isolation fused spur inside the house and is protected by the RCD of the consumer unit. Is this correct?
No he quoted you a higher price cable and used a cheaper one
 
  • Agree
Reactions: suffolkspark
I've never come across that before, do you have any examples?
SWA is not suitable for long term immersion in water and most state this, but I've not yet seen reference made to wet ground or lawns.

It does make some sense, but it's hard to know how wet is too wet.

Here’s one such piece I read on the subject;

You’ll note it suggests MDPE Sheathed Cable as more suitable for water logged soil.
 
  • Like
Reactions: DPG and Jim_e_Jib
  • Funny
Reactions: DPG
Here’s one such piece I read on the subject;

You’ll note it suggests MDPE Sheathed Cable as more suitable for water logged soil.

Interesting, MDPE seems like a logical choice as it's used for water and gas pipes, though I'm sure it comes with it's own set of problems.

Yellow MDPE gas pipes aren't allowed to be exposed to sunlight due to UV degradation, so I wonder how much better a black cable would be?

Maybe it's time to bring back lead sheathed cables for direct burial
 
Thanks all, it’s a H6242Y cable in a black hose. Photo attached...
Mary
 

Attachments

  • 62E87651-4524-4EF6-B6C9-CE0BDCB3A852.jpeg
    62E87651-4524-4EF6-B6C9-CE0BDCB3A852.jpeg
    171.5 KB · Views: 61
  • 62820758-35A2-4B80-B2A9-4D59B19FA549.jpeg
    62820758-35A2-4B80-B2A9-4D59B19FA549.jpeg
    91.9 KB · Views: 56
Rough as! And its not an armoured cable you were priced for
 
  • Like
Reactions: DPG
That is not armoured cable, its twin and earth cable that would normally be used for the internal wiring of houses.

The flexible conduit is not a cable duct suitable for providing sufficient protection to a buried cable to negate the need for an earthed armour.
 
Just out of interest, how deep has the electrician put the cable in the ground?
 
Thanks all, it’s a H6242Y cable in a black hose. Photo attached...
Mary

That would be coming straight out if it was me.
 
  • Winner
Reactions: ferg and Spoon
Thanks all, he is also providing Part P certification, could he do that if he wires it like this? I mean, is it legal? From your replies it seems as though it’s not ?
It’s buried about 2 inches down, I think.
 
It does not comply with requirements. And at only 2 inches down that is a real worry. A spade would go straight through that.
 
  • Agree
  • Like
Reactions: Spoon and ruston
It does not comply with requirements. And at only 2 inches down that is a real worry. A spade would go straight through that.

Not much room for warning tape either, never mind the flora has survived.
Was there a vast difference between quotes?
 
  • Like
Reactions: DPG
He was quite a bit cheaper, I’ll speak with him and say that I’ll pay more for armoured cable.
Thanks everyone, I’m so glad I asked!! x
 
  • Like
Reactions: DPG and ruston
How much did he charge?
 
It’s buried about 2 inches down, I think.


He was quite a bit cheaper, I’ll speak with him and say that I’ll pay more for armoured cable.
Thanks everyone, I’m so glad I asked!! x

The cable needs to be buried at least 500mm (20 inches) deep, with warning tape above the cable. Any shallower is against the regs.

I can understand why he was so cheap now.......
 
That is verging on a DIY job not something you would expect from a qualified tradesperson.
 
I agree , but I though we had to tone down our comments now. I am pleased you said that.
I can see that maybe misconstrued. I was aiming it at the electrician not the OP.
 
  • Like
Reactions: DPG and ruston
I can see that maybe misconstrued. I was aiming it at the electrician not the OP.
No I understood that . I was referring to the work too.
I thought at the change in the forum it applied to the criticism of the standard of work posted too.
The OP can only take a quote at face value. I gave her post a like as she had the sense to know something is wrong , and her manners to say thank you.
 
  • Like
Reactions: westward10
that conduit is cheep pvc conduit and has no mechanical protection at all.
as above, I am concerned about the corners this "tradesman" is willing to cut just to save £5

working on 2.5mm cable as its coming from a spur.

swa cable £1.50 to £2 per meter 10m of is £20 tops

giving excellent protection for direct burying


or what you have got
twin and earth £0.50 per meter £5
pvc conduit 10m contactor pack £10

there is no need in my opinion to consider anything other than swa armoured cable for this application, especially as its a short run of small cable and the cost difference of cables are negligible.

I would not recommend paying more to change the cable type.

is this electrician registered with a part p scheme?
[automerge]1575475132[/automerge]
elecsa_fig_1.jpg
 
Last edited:
He was quite a bit cheaper, I’ll speak with him and say that I’ll pay more for armoured cable.
Thanks everyone, I’m so glad I asked!! x
If they quoted for armoured cable then that's what you should get.

I'd honestly consider getting rid of this tradesman though because that work is rough as old socks, non compliant, and I would not have any faith in any work they do after this.

Any electrician knows this is totally unacceptable and unsuitable, so they either don't know their job or are trying to pull a fast one. Both reasons would have me not wanting any further work from them.
 
@Mary1234 , How much was the quote for this work?
Do you have the quote in writing or was it a verbal quote?
 
If they quoted for armoured cable then that's what you should get.

I'd honestly consider getting rid of this tradesman though because that work is rough as old socks, non compliant, and I would not have any faith in any work they do after this.

Any electrician knows this is totally unacceptable and unsuitable, so they either don't know their job or are trying to pull a fast one. Both reasons would have me not wanting any further work from them.

That’s sometimes hard for some people to do. What’s the OP to do, tell her electrician she’s been on a forum, and they reckon your work is pants, halfway through the install. He/she might think they are being had over.

Unless the OP is of the confident type :), she might ask the electrician to qualify his work, she was quoted for and expected swa cable. Get him to prove what he’s doing is correct. Ask him to email his scheme etc. Just my opinion.
 
If hes with a scheme check his membership out against said part p body, you could even tell them your concerned about some work one of their members is currently doing to get them to take a look?
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
External Electrics, cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38

Advert

Thread statistics

Created
Mary1234,
Last reply from
suffolkspark,
Replies
38
Views
4,096

Advert