- If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
- United Kingdom
- What type of forum member are you?
- Heavily Qualified Electrician / Teacher / Tutor - etc
They both meet the requirements of BS6004, for abrasion resistance tests, they are tested as a complete product, inner cores are suitable for being contained within an enclosure.PVC T&E and PVC singles are both manufactured to BS6004 and it would be assumed the insulation of the copper conductor is of an equivalent. If the sheath of the T&E is removed then it should be correctly contained as with singles after all the sheath is removed at accessories and within distribution boards.
However there is no testing or approval for taking a cable apart and drawing its unprotected inner cores through conduit.