Tomking

Hi I just start job need help with description whats wrong wit neural
20211005_133837.jpg
 
No neutral from bottom of second DP switch to neutral bar. I'm guessing an RCD has been replaced at some point due to nuisance tripping?
 
TO MANY UNNECISARRY LONG WIRES
 
  • Like
Reactions: Megawatt
nothing wrong that a complete strip down and rewire won't fix. that's a rat's abortion.
 
old split load board with trippy rcd , so some clever sparks swapped out the rcd for a main switch , seen this loads of times
 
my guess is that they re-used the old splt board when rewiring and it tripped out so they took the easy option
 
Rcd trips cos they put rcd on main neutral bar on split board 3netral bars main rcd1 rcd2
Sorry, but could you start again.

what have You been asked to do in this job?
and
what is your question?

edit: sorry sent post before I saw above post.
 
Having a main switch instead of the RCD is not immediately dangerous or potentially dangerous.

there are issue that can be coded due to inadequate additional protection, but I can’t see the main switch being a Code in itself. What do you think?
 
Having a main switch instead of the RCD is not immediately dangerous or potentially dangerous.

there are issue that can be coded due to inadequate additional protection, but I can’t see the main switch being a Code in itself. What do you think?
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem
 
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem
Just ask yourself is this issue immediately dangerous? Is someone in imminent danger?
or is there a potential danger? Could some one come to harm if some one does something?

ask yourself if the double pole isolator without a neutral is dangerous and how is it dangerous? Justify your coding.

I don’t like it, I think it’s wrong. just because I don’t like it and think it’s wrong doesn’t mean I can code it. I can’t just say it’s wrong. you have to give a valid reason why it is electrically wrong.

so what do you think? Does it need coding? And why?
 
Dunno never seen switch with no neutral so Dunno how to code this also rcd sometimes tripping on zs low 3lead test is neutral arrangements can cause that or earthing problem I put as earthing problem

What was the earthing problem?
 
  • Like
Reactions: Deleted account
You are carrying out an EICR?
Your profile has you down as a trainee.
 
Just ask yourself is this issue immediately dangerous? Is someone in imminent danger?
or is there a potential danger? Could some one come to harm if some one does something?

ask yourself if the double pole isolator without a neutral is dangerous and how is it dangerous? Justify your coding.

I don’t like it, I think it’s wrong. just because I don’t like it and think it’s wrong doesn’t mean I can code it. I can’t just say it’s wrong. you have to give a valid reason why it is electrically wrong.

so what do you think? Does it need coding? And why?
Q
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Whats wrong with this pic
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
39

Advert

Thread statistics

Created
Tomking,
Last reply from
telectrix,
Replies
39
Views
2,685

Advert