That's to be expected though isn't it?And all the circuit Zs readings are waaay below Ze value ?! Were these measured with all the bonding connected ?
I had to look at that… the BS number suggests MCB, but there’s RCD trip times. Wasn’t until I noticed the times were all the same that I realised.The tester apparently didn't even know what voltage he/she was doing the IR testing at, or any mention of how they've managed to get RCD test results when there's no RCD mentioned, and presumably don't know where to find max zs values in bs7671 as they are N/A as well.
So why aren't they listed at the top of the certificate then? The cert is a load of crap.I had to look at that… the BS number suggests MCB, but there’s RCD trip times. Wasn’t until I noticed the times were all the same that I realised.
Must be a dual rcd board,
I certainly would do this for clarity, and I know what you mean, but is there an absolute requirement to list the two RCD's on their own line?So why aren't they listed at the top of the certificate then?
I was thinking the " characteristics of this db" section, "associated RCD's". Would you not use that?I certainly would do this for clarity, and I know what you mean, but is there an absolute requirement to list the two RCD's on their own line?
Ultimately we are listing final circuits and what is protecting each one.
No, as that is "Complete only if not connected directly to the origin", i.e. a sub mainI was thinking the " characteristics of this db" section, "associated RCD's". Would you not use that?
Oh yeah, see that now. Good point.No, as that is "Complete only if not connected directly to the origin", i.e. a sub main
Napit's certifcates could be better worded in that part.
all depends on how deep you planted them.Normally, there is no voltage neutral to earth… so it’s possibly not an option on these testers.
Looks like VIR tails between cutout and meter which could do with being replaced, but that should be done if the meter is changed.
The test certificate doesn’t have a number for “points served”
How difficult is it to count light bulbs?
I must be having a thick moment ?! Thought Zs was Ze + R1&R2 ?That's to be expected though isn't it?
Interesting, by calculation yes, but would you take a Zs measurement without bonding connected?I must be having a thick moment ?! Thought Zs was Ze + R1&R2 ?
Zs isn't really applicable with a TT system as the RCD is providing fault protection, not the mcbs - they would never trip with 315 ohm earth rod.The tester apparently didn't even know what voltage he/she was doing the IR testing at, or any mention of how they've managed to get RCD test results when there's no RCD mentioned, and presumably don't know where to find max zs values in bs7671 as they are N/A as well.
Yeah I know... maybe I was over reacting. No excuse for the NA in the IR test voltage tho eh?!!Zs isn't really applicable with a TT system as the RCD is providing fault protection, not the mcbs - they would never trip with 315 ohm earth rod.
Nope, pure muppetry that one!Yeah I know... maybe I was over reacting. No excuse for the NA in the IR test voltage tho eh?!!![]()
Also, and not relating to the "issue" , that tester you are using has been recalled for safety issues.
If you contact fluke they will replace it.
Fluke SM100, SM200 and SM300 Electrical Socket Testers Voluntary Recall | Fluke
Fluke Corporation has identified a safety issue concerning the Fluke SM100, SM200 and SM300 Electrical Socket Testers. As a precautionary measure, Fluke has decided to voluntarily recall all of these products and provide affected customers with free replacement products.www.fluke.com
Yeah, there are a couple of options, neither are that good tbhThey won't directly replace it, but will send a T90 voltage tester.