Right here we go,

This is my first post on here :-). Installed a Wylex 17th Edition 15 way board at my own house. I put all the power on one side and lighting on the other. I'm not sure if this is how everyone else does it but im new to 17th boards so if you do otherwise please say. So... I turned it on as I normally do trying one Mcb at a time to see if any trip the RCD. All the lighint circuits are fine. But two of the rings trip it on the power side. So I unplug everything on the rings and turn it on. Seemed to be ok. Turned the living room tv on and it tripped. After fafing about all circuits are fine until put under a bit of load. Going around with a power drill any circuit on that RCD trips. The house is a older house and wiring my not be great but it has an extension on the back which I wired properly even that trips it.

Could this be due to having power all on one side and lighting on the other?
I know the neutrals are all in the correct bars.
Faulty RCD or just to much load for one side and needs to be spread over both the rcds?
My first idea around the problem is to upgrade the troubled RDC from 80amp - 30ma to 80amp - 80ma. So basically a less sensitive RCD?

Any Ideas?? Do you think my solution will work?
 
Paul are you a sparks??

Because I'm sure you have done something that is obvious, but did you test any circuits before you changed the board
 
This is a wind-up right ?

Please put it back in the box and take it back to the shop, you could then call your inspecting engineer and ask him what he thinks.
 
  • Like
Reactions: 2 people
Certainly looks like a linked/borrowed neutral problem, but what were your IR readings on the ring?
Normally circuits are split across the board upstairs power and downstairs lights and vice versa.

The RCD protection is there to prevent fatalities increasing the tripping current would bring it over the fatal level. RCDs do not come in 80mA, do not try this.
 
Paul, since you are not an electrician I'm assuming that you are also not a member of a domestic installer scheme in which case, are you aware that by carrying out this work you have contravened the building regulations and put yourself and others in danger?
 
He maybe in Scotland Trev,

but I think now the only advice I can give is you need help Paul so post your location and one of the lads will PM you and offer to sort this out for you
 
Paul, whereabouts are you? There are members of the forum all the way around the country and in Malcolm's and Engineer54's all over the world. I'm sure that one of us would be willing to help you out
 
Paul, take the advice of help as your and your families safety is paramount
 
  • Like
Reactions: 1 person
Thanks Richard!!! I found the fault. I was over confident in my own wiring and did not test the ring I added on. Was not getting continuity on the ring. So split the ring in half worked my way back to the problem. Was human error put the load of a spur into the mains side of the spur so it was constantly on. Which was causing the constant tripping. Thanks for the positive helpful comments! Dont worry trev I am going to get in signed of straight away... You live and you learn..... :)
 
There is nothing wrong with it! 25mm tails 16mm earth 10mm to both main gas and water. All rings are correct. Cable sizes are spot on and local means of isolation where needed throughout. Done cross bonding in bathrooms for extra precaution. Labled correctly I could go on... I worked with an electrical company for 6 years. Its just the first cu I have even done... I have not got around to doing the full course yet.
 
Last edited by a moderator:
Paul,
One swallow doesn't make a summer and working in an electrical company doesn't make an electrician?

With your opening statement about putting 'all the power on one side and all the lighting on the other' it suggests you are not a qualified spark? Electricity kills mate, please be careful. Presumably you are qualified to the 17th Ed Regs so you can fill in a certificate and that you have fully inspected and tested the work? - cont, IR Ze, Zs, PFC, RCD et al? The issue about the ring seams to indicate you hadn't tested the installation, which you are required to do.

On the basis you are in England or Wales how do you propose getting this signed off under Part P or are you going to pay for LABC to inspect it?

Please get someone qualified in to check the work and do a PIR/EICR for you.
 
  • Like
Reactions: 1 person
There is nothing wrong with it! 25mm tails 16mm earth 10mm to both main gas and water. All rings are correct. Cable sizes are spot on and local means of isolation where needed throughout. Done cross bonding in bathrooms for extra precaution. Labled correctly I could go on... I worked with an electrical company for 6 years. Its just the first cu I have even done... I have not got around to doing the full course yet.


just to be pedantic how did you test the rings??

Danny
 
OK maybe I'm having a blonde moment but what is "lmao"??

And back to the OP - an interesting division of circuits - not quite how I'd do it!!

Hi Murdoch,

It was my response to 'testing by drill' and it translates to 'laughing my --- off'
 
  • Like
Reactions: 2 people
THIS IS THE REASON that the country at large needs a means of controlling the sale of certain items. Threads like this make it self-evident.

I'm not saying that 'the usual suspects' should stop selling them, just that there needs to be a means of control. Like knives, glue, fireworks........ the list is fairly long.


I was in a wholesaler about an hour ago and a punter came in asking about how to replace a broken 3036 carrier, so they happily ordered him in one of the MCB converters....didn't ask him what rating, didn't tell him that you need to take the cover off the board (normally) to fit the receiver....all they wanted was the sale. And that was a wholesaler. Imagine what the pimple face youths in the orange shed do.
 
  • Like
Reactions: 3 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
17th Dual RCD Mcb order and have a strange fault Help!! lol
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
paul0547,
Last reply from
Rockingit,
Replies
25
Views
2,485

Advert