Doble89
I have installed two rcd sockets in a plant room where I work I done this using 2.5 swa cable on a 16amp rcbo as there sockets will rearly be used the length is 15 m long is this ok
I disagree,
if there is a neutral to earth fault which device would trip?
unless there is a time lagging device like you have in a site MDU,
either the RCD or RCBO could trip and could result in a headache later
I would suggest that you downgrade the RCBO to an MCB.
The SWA has earthed armouring so an RCBO is not require
Richard
I think the OP means the sockets are RCD protected by having used an RCBO. In which case all is well.
yes I understand that,
if there is a Neutral to Earth fault on the device that is plugged into the RCD socket then there are 2 Residual Current devices in series in the circuit.
As I stated before either of the RCD, or the RCBO could trip.
If my reading of the OP is correct then they aren't 'RCD sockets' - just normal sockets connected to an RCBO.
ok
I see what your saying.
if they are normal 13amp sockets being used as RCD sockets because they are protected by an RCBO,
yes I agree that would be ok
Sorry if I caused any confusion
I have read it about four times,it says to me,t he has run one swa 2.5mm fed from 1No 16amp rcbo, terminated to feed 2 No rcd sockets
Its a good enough confusing statement to compare with a lot of the regs
Doble - could you please enlighten us?!
Well Rockingit, at least we agree about somthing
I also don't disagree with you that if he HAS installed RCD sockets on an RCBO circuit then it's not a good solution!
Seeing as there's a lot of agreeing and dis agreeing going on
I will agree with dis agreeing, and disagree that I only agree just to dis agree
I thought it was just me that had been on the pop.......
Must admit, it reads to me that the socket-outlets are RCD type, and they are also protected by an RCBO.
Don't see the need for any RCD protection, unless the socket-outlets are to be used for mobile equipment outdoors?
Thats my thoughts Spin, are they for a specific purpose ? still no need for a RCBO and as it is plant room "skilled and instructed"?? as any one in there should either be trained, Skilled, and at least instructed,
Pict
16amp radial
Australia
Doble89,
the pict,