Octopus
I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket circuits.....
I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket circuits.....[/QUOTE
deleted due to brain not having woke up yet.
I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket
This is a 16th edition board and is original to the property. I am not asking on advice on how to bring to the 17th. I am asking why there would be a short between the service neutral and my TT earth. Can anyone shed any light on this as the distance to the transformer is quiet a way And thus should not pick up resistance to the earth point there. Has anyone had this before.
Thanks anyway murdoch.
I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket
This is a 16th edition board and is original to the property. I am not asking on advice on how to bring to the 17th. I am asking why there would be a short between the service neutral and my TT earth. Can anyone shed any light on this as the distance to the transformer is quiet a way And thus should not pick up resistance to the earth point there. Has anyone had this before.
Thanks anyway murdoch.
I was not suggesting how to upgrade to 17th... I was suggesting a way to possibly minimise inconvienience!
I would be recommending replacing the front end 30mA RCD with a 100mA and installing RCBO's for the socket
This is a 16th edition board and is original to the property. I am not asking on advice on how to bring to the 17th. I am asking why there would be a short between the service neutral and my TT earth. Can anyone shed any light on this as the distance to the transformer is quiet a way And thus should not pick up resistance to the earth point there. Has anyone had this before.
Thanks anyway murdoch.
Maybe not, but this is the second occasion you have been to this installation, and you Have previously carried out installation work to the property. A CU change would have been prudent advice to the customer at that time, rather than 2 years or so down the line. So when you do upgrade the present CU, replace that up front 30mA RCD with a 100mA S type, to give extra protection without nuisance tripping to this TT installation. A straight 100mA RCD will not work, most faults will take out both the 30mA and the 100Ma RCD's....
As for your problem, it's just a case of breaking things down and testing until you can isolate where the connection lay's. Only methodical testing is going to reveal or point you in the right direction as to the cause!! Conduct a ramp test to find out, at what sort of leakage current is taking the present 30mA unit out.... Do you own/posses an earth leakage clamp tester??
Apon functional testing or circuits and then blanket testing between the neutral and earth bars inside the board I had a reading of 0.00Megohms. This is with the main switch closed (On) and all MCBS open (off).
Don't know if it will help, but can you measure N to E as a finite resistance, e.g. using the continuity range? Just wondering if there is some way an external fault e.g. in neighbours property and via gas/water bonding could be contributing in someway (not sure it's likely, but might be good to know).
Hi SJD, Yeah I thinks its service side as the fault disappears when the service isolator is opened. Bearing in mind this is TT, Close the isolator and then its 0.0Megohm between the neutral and earth bars in the DB....Its weird......