I've done the calculations and it comes out at 10mm but what Im saying would the first 10 meters be okay in 6mm. The first 10 meters works out less than a half a volt volt drop
I have a job where the client wants a 7kw car charger 50 meters away from his house. The problem is there is a 6mm that's been pre wired 10 meters through his house from the main consumer unit to an exterior wall and sealed up. So I would have to use that and join onto the 10mm exterior and put...
Okay just been speaking to some that said even in the worst case scenario on an unbalanced system the neutral current will not exceed the highest of the phase. So if it's a 30 amp circuit then the maxmima neutral current is 30amp.
So many different responses and its clear I'm not the only one...