  1. D

    Owed money....

    I have used (Thomas Higgins) online correspondence before it which gives him 14 days to respond to them why he hasn't paid. After 14 days they will send you a email to press take to court action. Which will happen the very next day and always use high court recovery. It worked for me I ended up...
  2. D

    UK Advice needed for garage power job

    sorry 0.22 my bad (trying to quote and not preproofing what i reply) 1578171172 i wasnt looking to get roasted here i just put something out there and asked them to check
  3. D

    UK Advice needed for garage power job

    i think we have covered to issue i miss abbreviated Ze as Zs
  4. D

    UK Advice needed for garage power job

    pme and ze at db1 if my memory serves about 22 omhs bottom end i couldn't rely on the swa cable earth so installed a rod and isolated the gland earth connection at garage to stop parallel paths
  5. D

    UK Advice needed for garage power job

    it was a long time ago and yes while being assessed working for someone else and i had the unlucky visit with the company manager aswell so never really looked into it. 1578170015 20a mcb at board db1 measured at db2 rewirable fuse metal clad board
  6. D

    UK Advice needed for garage power job

    i forgot to mention current ze is armour cpc
  7. D

    UK Advice needed for garage power job

    i never said forbid i got a dilemma for you 2 core swa installed in ground by house builder (major builder) already supplying a db in garage ze is 175 ohms what do you do? scenario customer wants a new consumer unit installed in the detached garage. main incomer to building is on other side...
  8. D

    UK Advice needed for garage power job

    niceic IF the outbuilding has NO exposed conductive parts & thus no introduced low resistance earth path then the PME can be exported. e.g. total wooden shed on support battens with no pipework entering the shed... This will meet BOTH of the above regs so OK exported. Obviously if the house...
  9. D

    UK Advice needed for garage power job

    western power is my area and ive been shoulder tapped by my governing body before on a visit tt allows for higher than 35ohms at db
  10. D

    UK Advice needed for garage power job

    due to not being allowed by dno to transport pme to other buildings and or high earth readings,
  11. D

    UK Advice needed for garage power job

    i would where it comes through the brickwork on house straight into ipbox sealed to allow swa via a cantenary wire with metal zips into either a small consumer unit dont forget to check whether you need to slam a rod in as tt for external outbuildings, you wont need rcd board in here if its...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock