    Motor Tripping RCD but it's not even connected to it

    SOLVED. Thanks to all of you who gave helpful suggestions. I went back yesterday afternoon and tested the IR on the new motor and was all good. So I then disconnected the neutrals of each circuit that was on the tripping RCD and found that with one of the lighting circuits disconnected the RCD...
  2. J

    Motor Tripping RCD but it's not even connected to it

    Also I think it is very unlikely that PME will be available.
  3. J

    Motor Tripping RCD but it's not even connected to it

    When I originally installed it the motor MCB was next to the RCD that trips and was in fact fed from the RCD. When we started the motor and the tripping issue arose I moved the MCB away from the RCD and as stated previously I have fed it from the main switch. It is an MK metal clad board so not...
  4. J

    Motor Tripping RCD but it's not even connected to it

    @JD Hogg If it is a TT system how can you have circuits not connected to an RCD? There is a 100mA RCD before this board but this isn't affected.
  5. J

    Motor Tripping RCD but it's not even connected to it

    It is an induction motor, The RCD trips when the DOL start button is pressed It is for an apple press It is started with low (no) shaft load I have not taken IR measurements, as I said it's a new motor and even if there was a fault why would it trip the RCD?
  6. J

    Motor Tripping RCD but it's not even connected to it

    I don't have a photo of it but from left to right it is main switch, RCD 1 63A 30mA, 5 MCB's RCD protected, RCD 2 63A 30mA (this is the one that trips), 3 MCB's RCD protected, 32A MCB feeding motor, 16A MCB feeding different motor both 32A and 16A MCB's fed directly from main switch. Mainly old...
  7. J

    Motor Tripping RCD but it's not even connected to it

    Hi, I have just installed a dedicated 32A circuit to feed a motor which according to the data plate is 3.0kW and 16.6 Amps, single phase. It is fed from a 32A MCB via 6mm cable about 22 metres. I have fed it from a MK twin 63 Amp RCD board but this motor circuit is not protected by either RCD...
  8. J

    Trades to Site - a Warning

    OK I still haven't been paid or received a reply to my recorded delivery letter. Has anyone out there ever taken a company to small claims court? I'm not sure if it's really worth it?
  9. J

    Trades to Site - a Warning

    Just thought I would post a warning about this company, They are a facilities management company based in Oxfordshire and I got a call out of the blue from someone called Will Simmonds a couple of months ago. He wanted me to do a couple of jobs at an opticians in Bath, it actually fitted in with...
  10. J

    Which is the DNO earth block? PME

    Does anyone know if the DNO would have the answer?
  11. J

    Which is the DNO earth block? PME

    I don't have any photos, the tails coming from the original cut out now feed the CU and the meter has been moved to the outside meter box. The neutral and earth are still linked at both points. The work is to change CU so I am wondering whether to allow for running new earth cables back to...
  12. J

    Dodgy trade pictures for your amusement! - 1 Million Views!

    And here is why you should get an electrician not a plumber to wire your electric shower
  13. IMG_0995.jpg

    IMG_0995.jpg

  14. IMG_0996.jpg

    IMG_0996.jpg

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock