  2. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    I see your thinking now, so I won't code this. Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle. Thank you for your advice. Martin
  3. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    So I should code it as a C3 improvement recommended.
  4. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    There a four 3kw storage heaters on this board. So a load of 52 amps been drawn. So the load is under the 60 amp rating of the main switch.
  5. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    Haven't changed this board. I want to change it but need to discuss it with the owner but he doesn't like spending money.
  6. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    I was thinking the potential danger is the switching capacity isn't high enough in case of a fault.
  7. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    It's a shop and I had to pull the fuse to change the main board and this board is Economy 7.
  8. M

    Would you code a 60 amp main switch been fed from a 100 amp BS1361

    I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps. Im thinking this should be a C2, what are your thoughts please. Many thanks Martin
  9. M

    Induction Hob and Double Oven Diversity

    Thank you all for the advice. I've decided to quote the customer for a dedicated feed to the hob. many thanks Martin
  10. M

    Induction Hob and Double Oven Diversity

    They haven't purchased the induction hob yet and the oven is approx 10 years old.
  11. M

    Induction Hob and Double Oven Diversity

    Thanks for your replays. Its an existing kitchen that the gas hob has failed, so they are looking at upgrading to an induction hob and there's already a 6mm to the oven, so they are looking for the cheapest solution.
  12. M

    Induction Hob and Double Oven Diversity

    Could someone just check my maths and thinking please. Induction Hob 7.2kw = 7200/230 = 31.3 A Double Oven 6.6kw = 6600/230 = 28.7A Total Load = 60A Apply diversity 10A + 30% of remaining load 60 - 10 = 50 x 30% = 15A Diversivified load = 10 + 15 = 25A So a 6mm T&E on a 32A MCB will be ok...
  13. M

    Just spotted this.

    I saw this kit at the Home Building show last year. The batteries where 1.3 Ah NiCads. Didn't think they would last long in real life.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock