  1. P

    testing procedure for garage consumer unit

    this is the sort of reply i was expecting, not quite sure how this helps me, shame
  2. P

    testing procedure for garage consumer unit

    I'm in the process of fitting a CU in my workshop can anyone tell me do i do testing at the new 2 way CU as i would on a domestic one or the main one in the house or both? I was thinking both Before anyone says get a electrician in to do the job i'm a NICEIC domestic installer just not done...
  3. P

    Voltage drop on radial and ring

    Yes I've seen this but I'm using a 60898 breaker and that's not listed
  4. P

    Voltage drop on radial and ring

    So just follow the rules set out in appendix 15 of BS7671 100m2 for ring final and 50m2 for radial if using a 20A CB
  5. P

    Voltage drop on radial and ring

    What I'm trying to work out is the lb of 5 13amp sockets, I know how to work it out in a lighting circuit say 10 lights, 10 X 100 watts / 230 = 4.34 so lb of 4.34
  6. P

    Voltage drop on radial and ring

    I am try to work out the voltage drop, i have a radial circuit with 5 double 13amp sockets i just need to work out lb
  7. P

    Voltage drop on radial and ring

    when working out voltage drop on a lighting circuit to work out the amp's (lb)I don't have a problem, say 10 lights @ 100 watts each 1000 watts 4.35 amps but what should I apply for a ring final and radial circuit.
  8. P

    Low insulation resistance reading

    sorted, was a bad connection on the first ceiling rose i disconnected all the wires and put it back together and >299 reading
  9. P

    Low insulation resistance reading

    Basically I've done a test from the start of the first light fitting and the reading as should be +299 at 500v and disconetced cables at start of circuit and the reading is 1.7, we have had a mice problem recently so maybe it has been nibbled. The initial reading was low between line and neutral...
  10. P

    Low insulation resistance reading

    i've recently installed a new Consumer unit at home and will be using it as my first niceic assessment. I'm getting an insulation resistance reading of 1.7 on a lighting circuit in the osg it says minimum reading of 1 is this going to be ok? I've discovered what section of the circuit is giving...
  11. P

    Megger 1552 main dial selector repair required

    Can any one recommend somewhere other than megger I can get my MFT repaired. The main dial selector dial is starting to go, seems like a common fault with these.
  12. P

    Megger 1552 LOOP test problem <55v

    Hi i just got a megger 1552 from ebay and when select the loop function it bleeps and the <55 v flashes has anyone had the same problem or knows whats up with the machine, i've put new batteries in it.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock